I am a maintenance man but I do hold a journeyman's license I'll do my best to explain what is going on. I have 2 ea 50 Hp air compressor. one is approx. 2 yrs old (Com-05) the other is 20+ (Com-01). I seem to be having similar problems with both.
We are running 240 VAC 3 phase into the building to a 400 amp I-line from there a 150 amp breaker carries power to a 200 amp disconnect. with 150 amp fuses. from there it goes to a switch box that allows me to select which compressor I want to use. Com-01 the older one will run for 5-6 hrs. then it will trip the motor overload in the cabinet. by the time I get there (5 Min) I am able to reset the overload and it will run for a couple of more hrs. then it will do it again. During the cooler months we were able to run it for weeks then it started this as the temps started to rise. oil temps on the gauges seem well with in range. I have tested and replaced the temp switches they seem fine. I have replaced the motor starter with the overload and the thermal units. More recently we sent the motor out to a motor shop for evaluation . They did $1300 dollars of work to it. We reinstalled it on 6/30/21
and had the same result.. Com-05 runs most of the time but back in April while I was on vacation it tripped the breaker and blew one fuse, then the week after I got back it blew one fuse (not the same fuse) it has ran fine until 6/30/21 then it tripped the breaker and blew one of the fuses. I have done an amp draw on both compressors . Readings are A Phase= 100 amps B Phase = 87 Amps and C Phase= 88 Amps. All connections seem fine. I am at a loss
 
You might save a lot of time by connecting a logger to monitor the line currents and voltages. When a trip occurs you will be able to look back over the immediate history to see how these parameters moved from normal operation to abnormal.

One possibility is that there is something wrong with the supply, perhaps one phase sags or browns out, and the motor protection gear is not acting promptly to disconnect the compressor before the overcurrent kills the fuse. That would explain the similar problem on two different compressors, and possibly a seasonal variation due to changing demand on the power grid. The log should enable you to distinguish between this kind of situation and a regular motor overload from within the compressor.
 
I am a maintenance man but I do hold a journeyman's license I'll do my best to explain what is going on. I have 2 ea 50 Hp air compressor. one is approx. 2 yrs old (Com-05) the other is 20+ (Com-01). I seem to be having similar problems with both.
We are running 240 VAC 3 phase into the building to a 400 amp I-line from there a 150 amp breaker carries power to a 200 amp disconnect. with 150 amp fuses. from there it goes to a switch box that allows me to select which compressor I want to use. Com-01 the older one will run for 5-6 hrs. then it will trip the motor overload in the cabinet. by the time I get there (5 Min) I am able to reset the overload and it will run for a couple of more hrs. then it will do it again. During the cooler months we were able to run it for weeks then it started this as the temps started to rise. oil temps on the gauges seem well with in range. I have tested and replaced the temp switches they seem fine. I have replaced the motor starter with the overload and the thermal units. More recently we sent the motor out to a motor shop for evaluation . They did $1300 dollars of work to it. We reinstalled it on 6/30/21
and had the same result.. Com-05 runs most of the time but back in April while I was on vacation it tripped the breaker and blew one fuse, then the week after I got back it blew one fuse (not the same fuse) it has ran fine until 6/30/21 then it tripped the breaker and blew one of the fuses. I have done an amp draw on both compressors . Readings are A Phase= 100 amps B Phase = 87 Amps and C Phase= 88 Amps. All connections seem fine. I am at a loss
Are you saying that it’s blowing fuses in the control panel or your 200 amp disconnect ?
 
Is it a thermal type motor overload that's tripping? Does the cabinet have a ventilation fan and if so is it working?

I just had a fault on a large air handler unit where the motor thermal overload was intermittantly tripping do to high ambient temperatures inside the control panel because the ventilation fans were seized.
 
I have contacted our supplier on this issue and have had little success . I was looking at a monitor on Tuesday. I was out yesterday . I will look some more today. I want too thank you for all the responses so far
 
You might save a lot of time by connecting a logger to monitor the line currents and voltages. When a trip occurs you will be able to look back over the immediate history to see how these parameters moved from normal operation to abnormal.

One possibility is that there is something wrong with the supply, perhaps one phase sags or browns out, and the motor protection gear is not acting promptly to disconnect the compressor before the overcurrent kills the fuse. That would explain the similar problem on two different compressors, and possibly a seasonal variation due to changing demand on the power grid. The log should enable you to distinguish between this kind of situation and a regular motor overload from within the compressor.
Do you have a logger that you would recommend,
 
You have some useful current measurements. If, using your nomenclature for the supply lines A, B and C, you label the motor leads as say 1, 2 and 3, you have the following information on connections and currents:

(A B C) - (1 2 3) - (100A 87A 88A) ie A to 1, B to 2 and C to 3.

If now you rotate the supply lines 120 degrees:

(B C A) and connect these to (1 2 3) ie B to 1, C to 2 and A to 3 and now measure the three currents, - see attachment -

then:

(1) if the currents are now (87A 88A 100A) ie they correspond still with the supply lines A, B and C - the unbalance problem is with the supply;

(2) if the current are now (100A, 87A 88A) ie: they correspond with the motor leads 1, 2 and 3 the unbalanced problem is with the motor.
 

Attachments

  • usacomp.png
    26.4 KB · Views: 4
You have some useful current measurements. If, using your nomenclature for the supply lines A, B and C, you label the motor leads as say 1, 2 and 3, you have the following information on connections and currents:

(A B C) - (1 2 3) - (100A 87A 88A) ie A to 1, B to 2 and C to 3.

If now you rotate the supply lines 120 degrees:

(B C A) and connect these to (1 2 3) ie B to 1, C to 2 and A to 3 and now measure the three currents, - see attachment -

then:

(1) if the currents are now (87A 88A 100A) ie they correspond still with the supply lines A, B and C - the unbalance problem is with the supply;

(2) if the current are now (100A, 87A 88A) ie: they correspond with the motor leads 1, 2 and 3 the unbalanced problem is with the motor.
I'm not sure sure what this would do because I get the exact same reading on 2 different motors. I'm pretty sure that it is a supply issue but I am not sure what is causing it.
 
I would do the easy test I mentioned earlier but it is up to you what you do. It does help quickly point to a supply or compressor problem.

What are the 3 line to line voltages (or line to neutral voltages) at the motor terminals, at the output of the motor contactor, at the input to the motor contactor, at the input to the panel isolator, at the supply end of the panel feeder and finally at the source of supply to installation?

Quick sum. 50hp compressor on 3 phase 240V supply at say 0.8pf.

Balanced line current = (50 x 750)/(1.7 x 240 x 0.8) = 114A. So your figures appear 'low' too.

What I would do is measure the incoming supply voltages (line or phase) and currents with compressor off and then on to calculate the external impedance of the incoming supply. I would do the same at the output of the panel isolator and output of the circuit breakers, fuses and overload trips you mentioned to do some sums for the installation and panel wiring. For balanced line currents the line impedances need to be balanced too.

What type of motor starter? DOL or Star Delta or something else?
 
Last edited:
I am a maintenance man but I do hold a journeyman's license I'll do my best to explain what is going on. I have 2 ea 50 Hp air compressor. one is approx. 2 yrs old (Com-05) the other is 20+ (Com-01). I seem to be having similar problems with both.
We are running 240 VAC 3 phase into the building to a 400 amp I-line from there a 150 amp breaker carries power to a 200 amp disconnect. with 150 amp fuses. from there it goes to a switch box that allows me to select which compressor I want to use. Com-01 the older one will run for 5-6 hrs. then it will trip the motor overload in the cabinet. by the time I get there (5 Min) I am able to reset the overload and it will run for a couple of more hrs. then it will do it again. During the cooler months we were able to run it for weeks then it started this as the temps started to rise. oil temps on the gauges seem well with in range. I have tested and replaced the temp switches they seem fine. I have replaced the motor starter with the overload and the thermal units. More recently we sent the motor out to a motor shop for evaluation . They did $1300 dollars of work to it. We reinstalled it on 6/30/21
and had the same result.. Com-05 runs most of the time but back in April while I was on vacation it tripped the breaker and blew one fuse, then the week after I got back it blew one fuse (not the same fuse) it has ran fine until 6/30/21 then it tripped the breaker and blew one of the fuses. I have done an amp draw on both compressors . Readings are A Phase= 100 amps B Phase = 87 Amps and C Phase= 88 Amps. All connections seem fine. I am at a loss
So for anyone who has been following on Tuesday (7/6/21) I got a call at home and was told that there was a power outage at work for 2.5- 3 hrs but the air compressor would not come on and had no display. I advised the lead man to check the breaker in the I-Line that controls the power to our compressor shed. When he returned to the phone he said that was it and air pressure was coming up. Wednesday I was out, so on Thursday I was told that they had replaced a transformer about 2 blocks from here. We have been told that we are the last business in this grid. so anything that happens upstream is going to affect us. Today 6/9/21 I went do some more testing under the direction of one of our fellow members. This is the results that I have now. Voltage coming into the disconnect in the compressor shed A-B Phase 234 VAC, B-C Phase 236 VAC, C-A Phase 237 VAC A - Grnd = 205 VAC , B - Grnd = 118 VAC, C- Grnd = 116 VAC Amp draw A - Phase = 110A,
B Phase = 112A, C Phase = 114 A Sorry for the long post but I want to make sure you have as many details as I can give you .
 
Line voltages and currents now look balanced. Phase voltages out of balance which makes me wonder if you have a weak or broken neutral if provided to your site and used. Is your incoming neutral connected to ground and if yes where? Measured line currents very close to what I calculated - 114A. Grateful if you would keep us updated.

ps: Is motor connected as 3 phase 3 wire or 3 phase 4 wire?
 
Last edited:
Just remembered your supply is 3 phase 4 wire open delta so phase to ground/neutral voltages are fine.
 

Attachments

  • AE5139DC-21DD-45C9-A4BC-D4DE2AAB0FA7.png
    54.5 KB · Views: 6
Last edited:
So it looks like my last communications was on 7/9/21. This morning (7/19/21) we switched back to the old compressor, to see what happens, I checked the Voltage and is as follows A-B = 233 B-C =235 A-C =232
Amp Draw: A=100A B= 101A C= 95A, A-Phase to GRND = 204 B- Phase to GRND = 115 C-Phase - GRND = 116
 
Thank you. Sorry for delay in replying. I looked up City of Temple. What sort of industry or business supports this city? I could not find out.
 
Thank you. Sorry for delay in replying. I looked up City of Temple. What sort of industry or business supports this city? I could not find out.We Build hydraic cylinders among other this . out competor is acroos town. there are are a couple of foundries with machinshops in the area. there are seveal diffrent tyes of bussineses in this area
 

Reply to Compressor issues in the USA area at ElectriciansForums.net

Similar Threads

Hi, I am looking for a connection diagram or sugestions for a 2.2Kw single phase motor to drive a compressor. The spec plate shows that it can be...
Replies
5
Views
753
Hello, Looking for some advice following a botched 3 phase upgrade today. Some background: Commercial unit originally fitted out (4 years ago)...
Replies
7
Views
583
Some advise or views would be appreciated. My supply is 100 amp single phase. I purchased my property 3 years ago or so, the owner prior to the...
Replies
29
Views
843
Hi Guys, We have a CNC router which uses single phase for the spindle, stepper motors and control box. This is all wired in and working...
Replies
10
Views
1K
Hi, I have lifetime experience (50+ years) in United States with basic knowledge of split phase 120/240 volts replacing wall switches and...
Replies
5
Views
472

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock