Hi,
I'm a self-build amateur - I'll be running cables and getting system sign-off/inspection by certified competent person, and am just working through circuit design basics.

I'm referring to Scaddan's 'Electric Wiring for Domestic Installers' (16th ed for 18th ed IET), which includes example for addition of kiln to existing house (pp88-93).
  • Existing total current 118A, with diversity is 100A, on an 80A fuse, 80A meter, 80A consumer unit.
  • New load (+kiln), with diversity is 137A.
I'm okay with all of the calculations presented (sizing tails, sizing MCB, cable, and shock risk &c.) but I don't understand how he concludes in his summary that "main fuse needs uprated to 100A"

He notes that existing tails are inadequate but if taking account of diversity on existing system results in a design load that's 20A over the fuse, meter, and CU ratings, surely that was all already needing upgraded, and the increased design load will need more than 100A capacity.

Is anybody able to explain? Is it in a table ? (I'm waiting on the 'Brown book' on-site guide)

thanks - JS
 
Hi,
I'm a self-build amateur - I'll be running cables and getting system sign-off/inspection by certified competent person, and am just working through circuit design basics.

I'm referring to Scaddan's 'Electric Wiring for Domestic Installers' (16th ed for 18th ed IET), which includes example for addition of kiln to existing house (pp88-93).
  • Existing total current 118A, with diversity is 100A, on an 80A fuse, 80A meter, 80A consumer unit.
  • New load (+kiln), with diversity is 137A.
I'm okay with all of the calculations presented (sizing tails, sizing MCB, cable, and shock risk &c.) but I don't understand how he concludes in his summary that "main fuse needs uprated to 100A"

He notes that existing tails are inadequate but if taking account of diversity on existing system results in a design load that's 20A over the fuse, meter, and CU ratings, surely that was all already needing upgraded, and the increased design load will need more than 100A capacity.

Is anybody able to explain? Is it in a table ? (I'm waiting on the 'Brown book' on-site guide)

thanks - JS
Take your figures, apply a diversity factor of about 0.4 and then decide
 
I suspect the suggestion of up-rating to 100A is based on the fact that is the maximum size you can normally get on a domestic single phase supply and not actually based on the calculation.


This nicely shows the difference between theory and reality.

In theory they need a bigger supply, which would almost certain be 3 phase as you almost never get single phase supplies over 100A.

In reality a 63A supply would be adequate in most cases.

Electricians need to learn both the theory and reality as both are important parts of the job.
 
Hi,
I'm a self-build amateur - I'll be running cables and getting system sign-off/inspection by certified competent person, and am just working through circuit design basics.

Have you made arrangements for getting it signed off already? This is not normally permitted/possible and generally very few decent electricians would be willing to take this on.

Certifying electrical work involves signing for 3 seperate stages of the job, design, installation, inspection and testing.
If you are designing and installing then you will have to sign-off those elements of the job and the electrician you employ will have to sign for the inspection and testing that they do.
 
Have you made arrangements for getting it signed off already? This is not normally permitted/possible and generally very few decent electricians would be willing to take this on.

Certifying electrical work involves signing for 3 seperate stages of the job, design, installation, inspection and testing.
If you are designing and installing then you will have to sign-off those elements of the job and the electrician you employ will have to sign for the inspection and testing that
Should be a good answer...if at all
 
Have you made arrangements for getting it signed off already? This is not normally permitted/possible and generally very few decent electricians would be willing to take this on.

Certifying electrical work involves signing for 3 seperate stages of the job, design, installation, inspection and testing.
If you are designing and installing then you will have to sign-off those elements of the job and the electrician you employ will have to sign for the inspection and testing that they do.
... and therein lies the issue: engaging a 'decent electrician' who not only turns up but even returns calls and is a competent enough joiner to route and rout cables and backboxes in CLT.
TBH, I don't want to be doing this either, but a combination of failed main contractor, Brexit, and COVID have meant that I've had to take on much more of this build than I'd ever anticipated. So I'm making the best I can of the situation - I can't secure a reliable sparky for design, or first or second fix, so I'm going with the one who's said he'll inspect and sign off my installation (and who I've worked with as 'mate' in the past) - it's far from ideal but, as is often mentioned in other contexts, this is where theory has banged up against reality.
 
... and therein lies the issue: engaging a 'decent electrician' who not only turns up but even returns calls and is a competent enough joiner to route and rout cables and backboxes in CLT.
TBH, I don't want to be doing this either, but a combination of failed main contractor, Brexit, and COVID have meant that I've had to take on much more of this build than I'd ever anticipated. So I'm making the best I can of the situation - I can't secure a reliable sparky for design, or first or second fix, so I'm going with the one who's said he'll inspect and sign off my installation (and who I've worked with as 'mate' in the past) - it's far from ideal but, as is often mentioned in other contexts, this is where theory has banged up against reality.
So why doesn't your matey sparky do the design, after all he will be the one to sign his name to it.

If your supply really isn't enough then you can always lock out for instance (the kiln) when the cooker is in use.
 

Reply to Confused by Scaddan example in Electric Wiring for Domestic Installers in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Had UKPN come out to a property recently to upgrade the main fuse from 60A to 100A but when they arrived they said that the supply cable which he...
Replies
9
Views
2K
I'm in the middle of preparing a quote for installing 12 x 3Kw and 4 x 2Kw halogen heaters in a church. The system design was provided by a...
Replies
27
Views
991
I'm practising EICRs on friendly locations as I'm still in training - technically done my 2391-52 but frankly need loads more practise. I've just...
Replies
11
Views
804
I'm planning a replacement for my existing domestic CU and would like to have it sanity checked before I get an electrician involved. The main...
Replies
33
Views
4K
Hi all, Just to be clear, I'm not looking for advice on upgrading but rather just clarification of our existing setup. We need to upgrade the...
Replies
12
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock