Discuss consumer unit replacement in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Reaction score
18
been to price a job today on initial chat with customer over the phone they described the job as 3 extra sockets, new cooker circuit install downlights and extractor fan in the bathroom and a new consumer unit. on arrival at the property first thing i noticed in the hallway was a wylex 16th edition split load cu. sockets already rcd protected spare way to connect cooker circuit too and easy replacement of upstairs lighting mcb with an rcbo when i questioned customer as to why they wanted a new consumer unit reply was because the other 3 electricians who quoted for the job all said we needed one! am i missing something here or are they all taking the pee
 
I think they're looking for extra work, to make the board '17th edition compliant' you'd only need a converter kit to install a extra RCD or (better and won't be much more expensive) add 2/3 RCBOs.
 
thats what i thought even if i was looking for extra work still wouldnt dream of changing consumer unit! allowed for 2 rcbos in price gave customer price there and then needless to say that as it was about 300 quid cheaper than everyone else they accepted
 
Good for you. I have had to convince at least a couple of customers a rewire not required as previous electricians had said they need one because of an older re-wirable board, all suggested with no testing whatsover!

Everyone needs to make a crust, but I like sleeping soundly at night as well lol
 
I was in the same scenario few weeks ago, turned up to a job after a phone call needing a rewire. Quick insulation test of l&n to cpc and was reading globally 47mo.When I asked why they wanted a quote the said last guy came to put a light up and said it needed rewire at the cost of £2500 and he didnt even ask to see DB. Winds you up it really does
 
thats what i thought even if i was looking for extra work still wouldnt dream of changing consumer unit! allowed for 2 rcbos in price gave customer price there and then needless to say that as it was about 300 quid cheaper than everyone else they accepted

I think your right actually, no need to replace the db as you mentioned.
 

Reply to consumer unit replacement in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

Hi All, I am in the middle of purchasing a small 1 bed flat in England, and have been sent a Domestic Electrical Installation Certificate by the...
Replies
1
Views
1K
Hi all. Customer asking me to fix 3 phase consumer unit on a new shop . Its brand new installation . He want to use every part of shops and he...
Replies
9
Views
3K
NICEIC Certification Scheme SPD on old consumer unit?
Under amendment 2 of the BS7671, there is now a requirement to fit an SPD as standard. I am due to install a new outdoor socket circuit on an...
Replies
2
Views
2K
Hi All I'm new here. I have just finished my NVQ and waiting to do my AM2. I have a question on selectivity as it has always slightly confused me...
Replies
5
Views
776
Hi, while carrying out an EICR at a farm cottage on Friday i came up against a problem early on. Whilst measuring the Ze the reading i obtained...
Replies
22
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock