Is the correct method for testing the continuity of the main bonding conductors with a long flying lead from the tester to the other end of the cable?
 
r2 is the earth path, with r1 being the resistance of the phase conductor.
with main bonding only the r2 is present
 
r2 is the earth path, with r1 being the resistance of the phase conductor.
with main bonding only the r2 is present

I think he wants to know why earth is called R2? not what is the R2?

The simple answer is because it is. Why is the phase conductor called R1?
I think it's because of the test that gets done ie. R1+ R2 which is your earth fault loop impedence test. If your circuit has a fault then the fault current travels down the cpc, which is what it's designed to do. You're therefore testing the impedance (resistance) of the phase conductor and cpc. hence R1 + R2.

I hope that makes cos it doesn't make sense to me.....:D
 
Last edited by a moderator:
R2 Yes it makes sense when used in the earth loop impedance terminology.

But to call it R2 when refering to the individual conductor can confuse.
 
Last edited by a moderator:

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
Continuity test of protective conductors
Prefix
N/A
Forum
Periodic Inspection Reporting & Certification
Start date
Last reply date
Replies
11

Advert

Thread statistics

Created
Richard3009,
Last reply from
pevvers,
Replies
11
Views
10,089

Advert