R

Richard3009

Is the correct method for testing the continuity of the main bonding conductors with a long flying lead from the tester to the other end of the cable?
 
r2 is the earth path, with r1 being the resistance of the phase conductor.
with main bonding only the r2 is present

I think he wants to know why earth is called R2? not what is the R2?

The simple answer is because it is. Why is the phase conductor called R1?
I think it's because of the test that gets done ie. R1+ R2 which is your earth fault loop impedence test. If your circuit has a fault then the fault current travels down the cpc, which is what it's designed to do. You're therefore testing the impedance (resistance) of the phase conductor and cpc. hence R1 + R2.

I hope that makes cos it doesn't make sense to me.....:D
 
Last edited:
R2 Yes it makes sense when used in the earth loop impedance terminology.

But to call it R2 when refering to the individual conductor can confuse.
 
Last edited by a moderator:

Reply to Continuity test of protective conductors in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

EICR picked up no continuity on cpc on 3 pendants fittings in a grd Floor Flat. Zs measured @ other pendants & complies. Different opinions on the...
Replies
8
Views
479
Hi there, Just a quick question. Does a main protective bonding conductor require UV protection when run outside? I am under the impression that...
Replies
3
Views
728
I had an interesting little job this morning. Three sockets in an extension were not working and haven't worked for quite some time (years). It...
Replies
0
Views
325
Hi All Happy new year to all! First post but long timer lurker, so thanks for all the previous help! Just wanted to clarify something I have...
Replies
7
Views
895
Hi everyone, I'm nearly on my AM2 test and really enjoy the industrial side of things so I thought I'd learn by asking. I recently came across...
Replies
1
Views
797

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top