Hi every one,

Wondering is anyone can help me with regard to this diagram please see picture attached.

How that looking to you, can I connect 10 X 250w panels in one array on one string this way?

Thank you 20121129_162058.jpg
 
presuming the inverter is ok with 10 x 37V (presumably) Voc and 10 x 30V Vmpp + 20% then yes that'd be fine.

if you're using it for battery charging though, then no absolutely not.
 
Inverter Fronius IG30 plus.
System split in 3 roofs, do you think I should be concern about last long dc cable not too long?
Fronius 30:

MPP voltage range 230 - 500 V DC

Max. input voltage(at 1000 W/m² / -10 °C in an open circuit)​
600 V DC


Max. input current 13.8 A DC
 
Valet - worse-case scenario for max PV string voltage is combined Voc plus a 1.15 multiplier (add 15%) to take into account Voc temperature coefficient impact at low temperatures (reduced temperature of modules gives an increase in voltage output).
 
Thank you your reply. Yes roofs are the same orientation and angle, cable 4mm.

What max distance for 4mm when becoms not ok?
 
(15% Gavin....) ;-)
yeah well, I like to er on the side of caution, particularly when giving interweb advice to someone in Aus.

I've no idea what temps they get there, and IMO 15% is a bit tight (we've installed a fair bit in Inverness and known it to be -20 outside and bright sunlight, which would give +14.85% Voc on most mono panels, which adding in the panel tolerances could well take it into over voltage territory if right at the limits - I assume the 15% rule of thumb was determined by southerners;))
 
Do you know if IG plus Fronius have polarity protection. Just in case if cables get mixed up they all black.
get yourself some red and blue tape*, mark up the leads at both ends throughout the circuit, solve the problem at source instead of risking it all on the reverse polarity protection... though I'd be amazed if the fronius didn't have it (not used em myself)




*I prefer to differentiate between DC and AC colour coding
 
Thank you for your advice Gavin.

Ill try tapes. In Aus temp where we are temp always 28+ so a bit hot and panels get hot as well. So we went for Panasonic 250 HIT. At one point Fonius 30 had reading 3499w on 2.5 kw system so do you think it was possible or it was inverter glitch. Or inverter stopped to overproduce
which may cause clipping.
Many electronic transformerless inverters clip the power automatically when it reaches a certain level. But this one has a transformer so potentially should be no limit?

Optimum output on this inverter as per manual is 3000w. I did check on Fronius manual and it has polarity protection. So in my case dos not mater if polarity was swapped? As long as not swapped on panels?

Thanx
 
What is the best way to test panels before installation on the roof. Iam planning to use multimeter with test cables for MC3 connectors on the ends. Any suggestions, precautions I should take? On Panasonic 250w
 
You can test the panels indiviually using an inexpensive meter so lang as it can take 10 amps and 50 V DC.
You do two tests
1) Voc = Volts OPen Circuit, i.e. just measure the voltage across the panel - depending upon the light conditions and so long as you line the panel up to the sun, you should get a reading similar to that on the Panel Specification Sheet.
2) Isc = Current Short Circuit, and yes we do mean short circuit make sure you put it thoruigh the 10 Amp shunt on the multimeter and join the ends together. ! DON't Us this to do the string test though, you'll blow it up! The current is HIGHLY dependant upon the light/sun's output though so don't worry if this is way off, a bright sunny day with the panel at the correct angle is the only time you'll get the Isc quoted on the Spec sheet and you'll need an Irradiance meter to check it anyway.

You may find it worthwhile to get a push switch rated at 10 Amps and put it in the circuit that way you wont be pulling apart a 'live circuit'

http://www.electriciansforums.net/a...-testing-does-everyone-really-do-dscf2621.jpg

When you've installed the string you should also do a Voc and Isc on the whole string - unless you've got a DC clamp meter don't do the Isc test, (7 or 8 amps at 300 or so volts..) also make sure your voltmeter is rated to 10 x Voc - and that is the reading you should be looking for. Be VERY careful with the DC cables after the panels are connected in a string you are working with very high DC voltages. You can get big sparks and bangs from shorted DC cables - just remember you can melt a screwdriver across a car battery and that's only 12V!!
 
Thank you for that respect to all.

That the multimeter I am going to use, do you think ist ok for the test?
Just going to attach MC3 connectors on the end.

AC VOLTAGE

  • Measurement Range 200V-600V
  • ±1.2% ± 10 digits
  • Overload Protection: 600VDC or rms

DC CURRENT

  • Measurement Range DC 2000-10A
  • ±1% of rdg ± 2 digits
  • Overload Protection: F 200mA/250V fuse (10A range unfused)

Purchased on ebay:
DIGITAL LCD MULTIMETER VOLTMETER AMMETER BUZZER AC DC METER OHM CIRCUIT TESTER | eBay
 

Reply to Diogram for 10 panels. in the Solar PV Forum | Solar Panels Forum area at ElectriciansForums.net

Similar Threads

Hello All and happy new year. Over the holiay I have changed all of my old sockets to some nice new ones and added a couple with usb sockets for...
Replies
4
Views
767
Hello, First of all, thank you in advance for any helpful insights posted in response to my question. I have just moved into a new home. With...
Replies
1
Views
1K
Hi all, Just to be clear, I'm not looking for advice on upgrading but rather just clarification of our existing setup. We need to upgrade the...
Replies
12
Views
1K
Hi all, Great to of found this forum. Much respect for keeping everyone safe! My background is in commercial data and Audio Visual. Been...
Replies
0
Views
534
guys i have a question regarding gse in roof trays (portrait) and ja solar 395w all black panels GSE say the 395's fit but they dont according to...
Replies
0
Views
930

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock