Discuss Disconnection time of external bulk head... in the Australia area at ElectriciansForums.net
Sparky12021986
i need your help please this question is going to be a long 1...
first let me explain the situation...
Electrical Supply
The electrical supply to the house is 230V, 50Hz, single phase and together with the installation forms part of a TN-C-S system. The electrical intake position is housed in a fibre glass enclosure adjacent to the front door, with external opening.
Electrical Installation
Distribution is by an 8-way consumer unit (C.C.U) which currently has 2 spare ways available. Existing overcurrent protection is provided by means of BS 3036, Semi enclosed (rewireable) fuses. The c.c.u is mounted at ceiling height on the inside wall directly above the electrical intake position.
The existing installation within the house and garage is wired in general purpose P.V.C insulated, P.V.C sheathed twin and earth and C.P.C multicore cables to BS 6004embedded within the fabric of the building. The extensio is to use the same wiring system and the 2 spar ways are to be used for dedicated lighting and power final circuits. Existing BS 3036 protective devices are to be replaced with Type B c.b.s to BS EN 60898.
All socket outlets are to BS 1363 and mounted 300 mm above finish floor level (f.f.l). All lighting switches are mounted at 1400 mm above f.f.l.
So after all that here is my question....
During the design stage, explain with reasons why you need to know the disconnection time of the external bulkhead type luminaire?
you need to know disconnection times to calculate Zs values and hence ensure disconnection times are met. ( 0.4secs. for any circuit < 32A ).
Strictly speaking its the disconnection time of the circuit supplying the external bulkhead luminaire. Sounds like an exam question!
my answer is not really to know what the disconnection time really is but why you need to know it... can you possible shed some light on the subject for me plz...
If you are happy with all the above explanations then the reason you should know the disconnection time is to demonstrate you are familiar with BS7671 and so that you can write it on the EIC!!!
If the question is why is it 0.4 secs as opposed to 0.2 or 5 seconds, that's a different question!
say the disconnection time for the circuit is 0.4 secs. you refer to the time/current graphs in bs7671 to see what PFC will cause the breaker/fuse to operate in 0.4 secs. then you need to calculate/measure the Zs to see if it will.
Knowing the disconnection time, will allow you to determine what size cable, and what type and size of CPD to use.
For instance, it used to be that lighting circuits only required a 5s disconnection time. This has been changed to 0.4 for TN, and 0.2 for TT.
So if you were replacing a CU, and the lighting circuits were all wired for 5s, then you may have to replace the wiring, install supplementary bonding, use a lower rated CPD, or use an RCD.
Reply to Disconnection time of external bulk head... in the Australia area at ElectriciansForums.net
Hello everyone, I hope nobody minds that my first post is a question. We have a bit of a situation brewing at home with regards to our new...
4K
Not come across this before, so would like some help, please. I went to install smokes and heat alarm (to new Scottish regs) in a fairly modern...
Hi all New to this forum, looks like a hive of information. I'm wanting to upgrade my garage electrics - I'm not a qualified electrician, hence...
Basic question to see if what I wish to do is correct: Client wants to build (or is building) and outside room (roughly 8m by 4m) to be used as a...