I had this problem a few years ago and after discussion with the NICEIC and the DNO, I haven't had it since...
However, Today I had a new 3phase service brought in to a DB that previously single phase on a submain.

The DNO had HV shut down this morn to upgrade the transformer, remove the single phase supply and install new 3phase cut out. Metering was booked in for late morn. By 1pm there was no show only to be told it would be later this afternoon. By 5 it still wasn't done, so the client called it in as an emergency. At 8, after ive left site, the metering guy turns up and says "sorry, I can't connect, there's no completion cert"

My client has just gone mental as I did on the phone to the metering guy....

I've done all 'dead tests' the certificate is all but completed, but I'm refusing to issue it without 'Live' test results.....
"its not complete until I have live tests results, phase rotation, functional operation etc etc, therefor I wil not issue completion cert" is my stance.
"I see completed certificates all the time and never have a problem" is the metering response.

So, what is everyone else doing? excluding test results from the first certificate for the DNO and issuing another upon connection?

Opinions please... before I result to violence
 
Some DNOs will accept a simple letter or note stating that the installation is safe for connection.
 
He wanted a 'completed' completion certificate...
Havent hand written certificates for years!!!
I know I could have given a certificate with all the relevant exclusions and limitations filled in, but seems crazy. Especially after waiting all day for the dopes... The client had no reference to requiring a cert in his paperwork. Bloody Western Power Distrubition...
 
Which energy company.? That would never happen with me. Its all self connect. I fit meters sometimes even before first fix,you lot can connect it all up with bell wire if you dare.The final connections on all new installs is down to the Electrician. (with us)
 

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
DNO want a completion cert on uncomplete install. What do you do?
Prefix
N/A
Forum
Electrician Talk
Start date
Last reply date
Replies
5

Advert

Thread statistics

Created
vxwestie,
Last reply from
7029 dave,
Replies
5
Views
73

Advert