Double pole isolation or switching on a TT system would be achieved by the main switch.

There is nothing wrong with installing single pole RCBOs on TT systems however if there was an s-type up front, you would need to install double pole RCBOs if RCBOs were specced for the job.
 
Double pole isolation or switching on a TT system would be achieved by the main switch.

There is nothing wrong with installing single pole RCBOs on TT systems however if there was an s-type up front, you would need to install double pole RCBOs if RCBOs were specced for the job.

Why D ?

Most upfront S-types are DP/Multi-pole anyway, I have seen these double up as the Isolator too, in fact on the model forms there are boxes to fill in where the RCD is used as a mains switch.

Just curious to your reasoning as to why you would need DP RCBOs in the above scenario where an upfront DP or multipole S-type RCD is used.
 
Why D ?

Most upfront S-types are DP/Multi-pole anyway, I have seen these double up as the Isolator too, in fact on the model forms there are boxes to fill in where the RCD is used as a mains switch.

Just curious to your reasoning as to why you would need DP RCBOs in the above scenario where an upfront DP or multipole S-type RCD is used.

N-E fault on the single pole RCBO protected circuit will take out the upstream type-s too. So much for minimising inconvenience in the event of a fault! lol
 
N-E fault on the single pole RCBO protected circuit will take out the upstream type-s too. So much for minimising inconvenience in the event of a fault! lol

Ah! Ok, good point, I have made the same case a few times on here myself about all SP RCBO boards as opposed to dual RCD boards, where they (SP RCBO's) won't isolate a N-E fault, no matter what the earthing system is, not just TT.
 
Last edited:
I think you can get them (at a price!) from the usual big three, ABB, Schneider and Siemens et al, along with a couple of others, but Wylex and other typical domestic types seem to be nearly all SP, or at least from the typical wholsalers off the shelf, the DP types you probably have to order.

I don't really see why it should be the case though, if I recall the DP ones did take up two modules width, but I am sure I saw an advert somewhere the newer DP ones were single module width (it may have been at the Elex show).

Edit: a quick Google shows some MK DP single module ones, also some Proteus ones.

Here is a Link to some ECD ones http://www.electricalcomponentsdirect.co.uk/acatalog/Compact_Mini_RCBO_Circuit_Breakers.html
 
Last edited:
Manufactors instruction leaflet states {on schneider electric rcbo)
Do not use on installations that require double pole switching eg IT or TT.
What they are trying to say is RCBOs are single pole and should not be used where double pole is required, They are not saying do not use on tt, why would they?
 
Think you'll find those RCBO's may well be SP+N rather than douple pole in the true sense of the meaning...

The description in the link states disconnection of both line and neutral upon tripping.
Never heard of this brand before. Interesting price too ! I might bear them in mind for the future.
 
The price seems too cheap, not sure if there is some catch, or it is a direct import from Asia without lots of markups. I'm almost tempted to buy one and test it, would be good to hear if anyone has actually used these.
 
They are similar price too Demans RCBOs for their Steeple range, although they are on SP. Only down side yo the ones linked is the supply needs wiring independently to it rather than just Busbar mount.
 
Ive used ECD RCBOs. They work fine & still do (regularly check the 30 odd I installed.) the test results for each RCBO were also "fine". There were a couple of out of the box non workers- new ones were sent immediately no questions asked.

But Ive had that with every make.
 
The description in the link states disconnection of both line and neutral upon tripping.
Never heard of this brand before. Interesting price too ! I might bear them in mind for the future.


Yes, but it'll be just switching the neutral, not DP in the true sense... Still serves the purpose though... DP RCBO's will have protection in both poles...
 
I’ve only got two RCBO’s in my flat, they’re coming out as soon as I get around to it.
I priced up Hager DP units, good job I was sat down when I saw the price. There’s bags of room in the board so a couple of MCB’s and a second RCD will be going in. It also means I can split the two rings between the two RCD’s. BTW it’s a 16[SUP]th[/SUP] board.

Before you ask, it’s how I found it when I moved in.
 
I’ve only got two RCBO’s in my flat, they’re coming out as soon as I get around to it.
I priced up Hager DP units, good job I was sat down when I saw the price. There’s bags of room in the board so a couple of MCB’s and a second RCD will be going in. It also means I can split the two rings between the two RCD’s. BTW it’s a 16[SUP]th[/SUP] board.

Before you ask, it’s how I found it when I moved in.

Are you sure you are competent to carry out this work?? :)
 
Oh dear Tony! Carrying out electrical work in a house without being NICEIC registered! Don't be suprised when the Part P police come a'knocking! A cowboy now as well as a Yorkshireman, it just keeps on getting better and better! :D
 
Oh dear Tony! Carrying out electrical work in a house without being NICEIC registered! Don't be suprised when the Part P police come a'knocking! A cowboy now as well as a Yorkshireman, it just keeps on getting better and better! :D

Shall we flip a coin or spin a bottle of something to decide which of us is going to grass him up? :devil:
 
Oh dear Tony! Carrying out electrical work in a house without being NICEIC registered! Don't be suprised when the Part P police come a'knocking! A cowboy now as well as a Yorkshireman, it just keeps on getting better and better! :D
but i am...and he rang me up asking if i`d do it for him....

which kind of blows geordie`s sly comment at #21 out of the water as well......:27:
 
but i bet you not got a harley davidson one. that's worth 3 "ordinary" ones.
 
What they are trying to say is RCBOs are single pole and should not be used where double pole is required, They are not saying do not use on tt, why would they?

I think they are......In a TT installation neutral is also classed as a line conductor,And as such if isolation to a particular circuit is required for maintenance or alteration we are supposed to be able to isolate both poles without having to knock the whole installation off via the mainswitch RCD. I am thinking that double pole CBs could be the answer(rather than dp rcbo's) I know that they are available,and you are still 30ma protected via main switch rcd. I'm a wee bit surprised mr Niceic hasn't made an issue about this before.
 
I think they are......In a TT installation neutral is also classed as a line conductor,And as such if isolation to a particular circuit is required for maintenance or alteration we are supposed to be able to isolate both poles without having to knock the whole installation off via the mainswitch RCD. I am thinking that double pole CBs could be the answer(rather than dp rcbo's) I know that they are available,and you are still 30ma protected via main switch rcd. I'm a wee bit surprised mr Niceic hasn't made an issue about this before.

Because it isn't an issue. DP isolation is all that is required on a TT installation, it doesn't say where. Also, a neutral is never a line conductor.
 
Oh dear Tony! Carrying out electrical work in a house without being NICEIC registered! Don't be suprised when the Part P police come a'knocking! A cowboy now as well as a Yorkshireman, it just keeps on getting better and better! :D

There's a way around it. As I'm retired I'll get Glenn to do it for me :bomb:
 
quote_icon.png
Originally Posted by mrloy99

. I am thinking that double pole CBs could be the answer(rather than dp rcbo's) I know that they are available,and you are still 30ma protected via main switch rcd. I'm a wee bit surprised mr Niceic hasn't made an issue about this before.

Far more sensible to have an all RCBO (SP+N) CU, than a couple of RCD's and a rack of DP MCB's, on a TT installation!!

Also have you considered the size that 10 circuit DP CU will be?? You'll be looking at providing at least a 26 way CU, including the DP isolation switch and 2 X RCD's, and that's not allowing for say a couple of spare ways for the future!! ...You won't be purchasing one of them for 50 odd quid!! lol!!
 
Last edited by a moderator:
Because it isn't an issue. DP isolation is all that is required on a TT installation, it doesn't say where. Also, a neutral is never a line conductor.

Sorry meant to say live..rather than line, neutral IS classed as a live conductor.
And without getting too ---- about the whole thing....We have to consider all possible scenarios.
We may wish to do work to a particular circuit without turning off the whole board.It is unlikely that all circuits have isolation after the board. eg lighting circuit with 2way switching
In TT situations neutral is not considered to have a RELIABLE connection to earth(unlike TN.where neutral and earth are joined at the service head)It is possible for the neutral to have a higher potential than earth .Removing the assumed neutral from the neutral bar is not recommended also due to a few possibilities,eg borrowed neutral or neutral in the wrong terminal in the neutral bar.
This voltage may only be a few volts and is unlikely to kill you but an unexpected tickle while working over the stairwell in a house could cause a fall.
 
Far more sensible to have an all RCBO (SP+N) CU, than a couple of RCD's and a rack of DP MCB's, on a TT installation!!

Also have you considered the size that 10 circuit DP CU will be?? You'll be looking at providing at least a 26 way CU, including the DP isolation switch and 2 X RCD's, and that's not allowing for say a couple of spare ways for the future!! ...You won't be purchasing one of them for 50 odd quid!! lol!!

Dunno about that!!!
The dp cb's I was using today(in an IT installation)were single module,same phisical size as normal cb's(general electric)
 
Dunno about that!!!
The dp cb's I was using today(in an IT installation)were single module,same phisical size as normal cb's(general electric)


That's true, but then most journeyman electricians don't know that they even exist.

I know that a guy is importing them from here (China) on another forum. How about giving us a link to these GE single module DP breakers, for everyone to see....
 
That's true, but then most journeyman electricians don't know that they even exist.

I know that a guy is importing them from here (China) on another forum. How about giving us a link to these GE single module DP breakers, for everyone to see....


i dont have a link but i could prob take a photo.They come inside these ips pre built bespoke panels made by a company called bender in uk.(I think they are german,but operate globally.)
 

Reply to don't use rcbos for TT in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hello, I have a hypothetical question (I'm an electrical engineer) to better understand RCBOs and how they are used in the USA. Let's say I would...
Replies
9
Views
1K
Trying to organise a CU replacement at home. It's a 1930s property. It's got a 10way CU but with no RCD protection. Was after a larger unit with...
Replies
65
Views
4K
Hi, I recently had an EICR done at my property which unfortunately was unsatisfactory. So the electrican advised a new fuseboard from BG General...
Replies
90
Views
4K
I had a call to a new customer who was experiencing what sounded like nuisance tripping on a kitchen ring. Some background first. It's an MK LN...
Replies
4
Views
786
I'm obviously still new and learning about what I can and cannot do, but essentially I want to install an EVSE at my own house for an electric...
Replies
8
Views
612

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top