Double pole isolation or switching on a TT system would be achieved by the main switch.
There is nothing wrong with installing single pole RCBOs on TT systems however if there was an s-type up front, you would need to install double pole RCBOs if RCBOs were specced for the job.
Why D ?
Most upfront S-types are DP/Multi-pole anyway, I have seen these double up as the Isolator too, in fact on the model forms there are boxes to fill in where the RCD is used as a mains switch.
Just curious to your reasoning as to why you would need DP RCBOs in the above scenario where an upfront DP or multipole S-type RCD is used.
N-E fault on the single pole RCBO protected circuit will take out the upstream type-s too. So much for minimising inconvenience in the event of a fault! lol
What they are trying to say is RCBOs are single pole and should not be used where double pole is required, They are not saying do not use on tt, why would they?Manufactors instruction leaflet states {on schneider electric rcbo)
Do not use on installations that require double pole switching eg IT or TT.
Think you'll find those RCBO's may well be SP+N rather than douple pole in the true sense of the meaning...
The description in the link states disconnection of both line and neutral upon tripping.
Never heard of this brand before. Interesting price too ! I might bear them in mind for the future.
SP+N is better than SP alone.
I’ve only got two RCBO’s in my flat, they’re coming out as soon as I get around to it.
I priced up Hager DP units, good job I was sat down when I saw the price. There’s bags of room in the board so a couple of MCB’s and a second RCD will be going in. It also means I can split the two rings between the two RCD’s. BTW it’s a 16[SUP]th[/SUP] board.
Before you ask, it’s how I found it when I moved in.
Oh dear Tony! Carrying out electrical work in a house without being NICEIC registered! Don't be suprised when the Part P police come a'knocking! A cowboy now as well as a Yorkshireman, it just keeps on getting better and better!
but i am...and he rang me up asking if i`d do it for him....Oh dear Tony! Carrying out electrical work in a house without being NICEIC registered! Don't be suprised when the Part P police come a'knocking! A cowboy now as well as a Yorkshireman, it just keeps on getting better and better!
but i am...and he rang me up asking if i`d do it for him....
which kind of blows geordie`s sly comment at #21 out of the water as well......:27:
oh so he told you did he?...More like Tony phoned your mother and she told you get round there and do it.
oh so he told you did he?...
only half the story as i was also told that if i didn`t i was to `get up them stairs without no tea`...
yeah...she has.I like your mother ... she has style.
my style comes across loud n clear in my posts & replies...didn't do a good job of passing it on though. :24::tank:
not much then against my..erm...5 i think ...at the last count...can't match that. i only got a couple of zippos.
well no...but i bet you not got a harley davidson one. that's worth 3 "ordinary" ones.
I do & so do you, you'll have to visit the other forum to see & purchase them though.....................Do you know of any manufacturers that make single module double pole RCBO's?
I do & so do you, you'll have to visit the other forum to see & purchase them though.....................
What they are trying to say is RCBOs are single pole and should not be used where double pole is required, They are not saying do not use on tt, why would they?
I think they are......In a TT installation neutral is also classed as a line conductor,And as such if isolation to a particular circuit is required for maintenance or alteration we are supposed to be able to isolate both poles without having to knock the whole installation off via the mainswitch RCD. I am thinking that double pole CBs could be the answer(rather than dp rcbo's) I know that they are available,and you are still 30ma protected via main switch rcd. I'm a wee bit surprised mr Niceic hasn't made an issue about this before.
Oh dear Tony! Carrying out electrical work in a house without being NICEIC registered! Don't be suprised when the Part P police come a'knocking! A cowboy now as well as a Yorkshireman, it just keeps on getting better and better!
There's a way around it. As I'm retired I'll get Glenn to do it for me
SBS supply trade only with true DP compact single mod rcbo's.You've lost me
Because it isn't an issue. DP isolation is all that is required on a TT installation, it doesn't say where. Also, a neutral is never a line conductor.
Far more sensible to have an all RCBO (SP+N) CU, than a couple of RCD's and a rack of DP MCB's, on a TT installation!!
Also have you considered the size that 10 circuit DP CU will be?? You'll be looking at providing at least a 26 way CU, including the DP isolation switch and 2 X RCD's, and that's not allowing for say a couple of spare ways for the future!! ...You won't be purchasing one of them for 50 odd quid!! lol!!
Dunno about that!!!
The dp cb's I was using today(in an IT installation)were single module,same phisical size as normal cb's(general electric)
That's true, but then most journeyman electricians don't know that they even exist.
I know that a guy is importing them from here (China) on another forum. How about giving us a link to these GE single module DP breakers, for everyone to see....