i am doing work in a void property for the council, there are downlights installed into a wet wall ceiling in the kitchen ( put in by previous tennant ) they are wanting to keep, when going round each downlight the earths were chopped away so went round sorted them all but i am getting no earth still so where they have joined from the original light position they have probably not joined the earth, the lights are wired through conduit with earths and the conduits earthed, and theres an earth going up to the light at the switch, i was wanting the ceiling down to get to the joint at the original light position but doing that would probably burst the wet wall and they would have to put a new ceiling up, the niceic inspector for the housing said that you can take a 4mm bond from the pipes in the boiler cupboard in the kitchen to the lights to give it an earth is this ok to do ?
 
I would try and get a CPC from the lights to the switch position if at all possible but if you can't then a 4mm to a suitable point to get continuity would suffice.

A note on the certificate and labels on the DB and CPC to make it easier for future works would also be advisable.
 
An extraneous conductive part maybe used as a protective conductor as long as it satisfies regulation 543.2.6.
Note a requirement is that the pipework is an extraneous conductive part and the cross sectional area shall be large enough or equal to applying regulation 543.1.1 which is sizing of protective conductors.

Best off reading regulation 543.2.1 and 543.2.6
 
  • Like
Reactions: Vortigern and Rpa07

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
Downlight earthing For housing
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
2

Advert

Thread statistics

Created
JM ELECTRICAL,
Last reply from
Ian1981,
Replies
2
Views
1,318

Advert