hi all
job this morning downstairs /landing lights not working ...lights flickered and went off last night ( trip stayed on)..mcb working (another circuit connected to it works fine) tested this morning (no cpc ) joined line and neutral at board tested at ceiling rose continuity ok .. but no power to any points
any advice what to check for ?
 
hi all
job this morning downstairs /landing lights not working ...lights flickered and went off last night ( trip stayed on)..mcb working (another circuit connected to it works fine) tested this morning (no cpc ) joined line and neutral at board tested at ceiling rose continuity ok .. but no power to any points
any advice what to check for ?
It will be the same circuit if it's connected to the same OCPD!
 
  • Like
  • Agree
Reactions: Risteard and DPG
Not 100% sure on what you are saying here. Do you have continuity on line and neutral from supply to the roses that are not working? Continuity tests will find this problem.
Is it 3 plate, or neutral at switch?
 
ok .. that light is only a metre away and can follow cable(only feeding that 1 light).....i was trying to say mcb working ....what do you advise i check for next
 
Not 100% sure on what you are saying here. Do you have continuity on line and neutral from supply to the roses that are not working? Continuity tests will find this problem.
Is it 3 plate, or neutral at switch?


3 plate at rose...continuity on line and neutral at roses that i checked but no power ....surely if continuity ok power should be there
 
You can't have continuity of the line and neutral supply or else the light would be lit!
 
  • Agree
Reactions: SparkyChick
Quick lesson... ohms law... voltage drop is proportional to the current flowing. Under load a high resistance joint may drop enough to prevent the lamps from lighting (depending on the type of lamps).

Depending on what test equipment you are using, it may or may not reveal high resistance joints... depends how much current it uses. So, if you're using a continuity function on a multimeter or AVI, it's not likely to provide reliable results... you should use the low ohms mode of an MFT or suitable stand alone meter as this will use quite a high test current (high test current = bigger voltage drop on small resistances).
 
  • Like
Reactions: Rpa07 and DPG
Should have added, working systematically, work your way along the circuit checking for loose connections (physically and visually) and testing the resistance of each conductor (using a long lead test back to the CU). Pay particular attention to any lights that are not ceiling roses as these are likely to have concealed junctions or choc block attrocities.
 
  • Like
Reactions: DPG
Have you got line continuity at the switched terminal at the rose.
 
agreed ...but i have and its not
What else is protected by the OCPD controlling the lights that aren't working. Reconnect the leg that you have dissed and as SC says check lights and switches for loose or broken connections.
 
  • Like
Reactions: DPG
It may be a stupid answer but have you actually operated the switch when testing.

The way I read it was that you have continuity between loop live and neutral and not switched live and neutral.
 
  • Funny
Reactions: DPG
I was going to state what is above aswell. Are you testing at the switch side of the celing rose? Not the loop in the middle? Also have you checked the continuity of the flex drop aswell as there may be a loose wire in the drop its self and are you sure the drop is not damaged. Try changing it.
 
Unlikely to be a switch drop, as all the lights on that circuit have gone out. Time to start again with the continuity tests.
 
  • Agree
Reactions: SparkyChick
Hum .... interesting.

Linking L & N and using a meter is the best approach, so:

Did you make notes of the readings from different fittings?

Have you tried the same with the neutral not linked at the CU? This may sound odd but you may have a parallel path via another neutral.
 
hi all
job this morning downstairs /landing lights not working ...lights flickered and went off last night ( trip stayed on)..mcb working (another circuit connected to it works fine) tested this morning (no cpc ) joined line and neutral at board tested at ceiling rose continuity ok .. but no power to any points
any advice what to check for ?
What meter were you checking continuity with?
 
Is there a value associated with the ‘continuity’ you have tested?
Personally I have a few different testers having very different toloetances as to what they would show as being ‘continuity’ in the sense you are using the word.
 
  • Agree
Reactions: SparkyChick
Have you checked for voltage between phase and neutral at the luminaire?
 

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
downstairs lights looking for advice
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
17

Advert

Thread statistics

Created
scott 123,
Last reply from
Risteard,
Replies
17
Views
2,454

Advert