Hi All,

Just a quick question, I need to get my gas & cooker installers to check earth and bonding conductor presence and sizing, (reg 132.16) what tool, if any, would you recommend? Such as a cable gauge or caliper etc.
What do you guys use, apart from your eyes and experience?

I' d appreciate you suggestions.

Thanks in advance.
 
try and get some known sizes of earth cable then offer them up to the existing earth cable for a good indication.

electrical wholesalers should have some off cuts they can give you.
 
Not really the response I was looking for! I thought this forum was to help each other? (see forum's statement below)

(Please be reminded that if your reply can't help the original poster, it may be seen as pointless and taking the thread off topic. Please make sure what you are about to post is in-keeping with the forum rules, specifically the "be nice" rule. Just be nice and helpful (even to new members) or don't reply at all please. Also note that we urge all members, regular or new, to report any posts that are off-topic, pointless or offensive)


Just to re-clarify:

I have a team of cooker installers who need to confirm earth & bonding sizes, I have the skills to do so, but I am in an office, I cannot expect a cooker installer to know how to, hence the question.
 
Not really the response I was looking for! I thought this forum was to help each other? (see forum's statement below)

(Please be reminded that if your reply can't help the original poster, it may be seen as pointless and taking the thread off topic. Please make sure what you are about to post is in-keeping with the forum rules, specifically the "be nice" rule. Just be nice and helpful (even to new members) or don't reply at all please. Also note that we urge all members, regular or new, to report any posts that are off-topic, pointless or offensive)


Just to re-clarify:

I have a team of cooker installers who need to confirm earth & bonding sizes, I have the skills to do so, but I am in an office, I cannot expect a cooker installer to know how to, hence the question.
well if YOU know how to do it why don't YOU tell them?
 
Hi All,

Just a quick question, I need to get my gas & cooker installers to check earth and bonding conductor presence and sizing, (reg 132.16) what tool, if any, would you recommend? Such as a cable gauge or caliper etc.
What do you guys use, apart from your eyes and experience?

I' d appreciate you suggestions.

Thanks in advance.

Measure the end to end resistance and the length, then look up the csa in the appropriate cable resistance table. :)
 
Not really the response I was looking for! I thought this forum was to help each other? (see forum's statement below)

(Please be reminded that if your reply can't help the original poster, it may be seen as pointless and taking the thread off topic. Please make sure what you are about to post is in-keeping with the forum rules, specifically the "be nice" rule. Just be nice and helpful (even to new members) or don't reply at all please. Also note that we urge all members, regular or new, to report any posts that are off-topic, pointless or offensive)


Just to re-clarify:

I have a team of cooker installers who need to confirm earth & bonding sizes, I have the skills to do so, but I am in an office, I cannot expect a cooker installer to know how to, hence the question.


well explain to them how to do it then.
 
Got to be a wind up, Cooker installers wtf is that, are the "Cooker installers" going to check the main water bond as well? the OP ought to furnish his "Cooker installers" with a MFT to check, oh sorry you need to go on a course to do that, "Cooker installers" my bottom.
 
Heres the answer for you then.

Firstly you need to check that the pipes are exteanepus conductive parts ( the test for this is explained in GN8). Now as this requires you to disconnect any bonding conductors you need to safely isolate the whole supply to the installation, but you know how to do thos already dont you?

If it requires bonding

Use the correct meter (according to GN3) to check the end to end resistance of the cable, now this has to be done with cable disconnected at both ends and with the whole supply still isolated from previous test, the result must then comply with the value within GN8

The cable must then be correctly sized for the earthing system in place and size of the incoming neutral.
 
A cooker installer, is an installer who can safely install electric, gas and dual fuel cooking appliances.
All of them have a MFT (Fluke 1652) and perform polarity, EFLI pre and post installations, but they are now expected to confirm reg 132.16.

I don't get the negative posts here, I just was looking for some pointers to make their lives a bit easier.

Why all the negatives vibes?
 
Heres the answer for you then.

Firstly you need to check that the pipes are exteanepus conductive parts ( the test for this is explained in GN8). Now as this requires you to disconnect any bonding conductors you need to safely isolate the whole supply to the installation, but you know how to do thos already dont you?

If it requires bonding

Use the correct meter (according to GN3) to check the end to end resistance of the cable, now this has to be done with cable disconnected at both ends and with the whole supply still isolated from previous test, the result must then comply with the value within GN8

The cable must then be correctly sized for the earthing system in place and size of the incoming neutral.
yeah exteanepus, that'll really throw him lol
 
A cooker installer, is an installer who can safely install electric, gas and dual fuel cooking appliances.
All of them have a MFT (Fluke 1652) and perform polarity, EFLI pre and post installations, but they are now expected to confirm reg 132.16.

I don't get the negative posts here, I just was looking for some pointers to make their lives a bit easier.

Why all the negatives vibes?


Because you should be capable of teaching them how to do this if your claim earlier is correct.
 
A cooker installer, is an installer who can safely install electric, gas and dual fuel cooking appliances.
All of them have a MFT (Fluke 1652) and perform polarity, EFLI pre and post installations, but they are now expected to confirm reg 132.16.

I don't get the negative posts here, I just was looking for some pointers to make their lives a bit easier.

Why all the negatives vibes?

I hope they carry out all the dead tests too and in the correct order, and understand the results also.
 
if these cooker installers are expected to check earthing and bonding, then they should have been trained how. you could help by telling them where the connections are if they are not obvious.
 
I could easily quote from a GN etc, but those publications are intended for a competent person.
Perhaps I should teach them all the adiabatic calculation?
 
I could easily quote from a GN etc, but those publications are intended for a competent person.
Perhaps I should teach them all the adiabatic calculation?


But thats what they need to learn and understand, theres more to electrics than just this cable will do attitude.
 
I have a team of cooker installers who need to confirm earth & bonding sizes, I have the skills to do so, but I am in an office, I cannot expect a cooker installer to know how to, hence the question.

This section of your earlier post is really confusing me. Firstly you say these cooker installers need to confirm earthing and bonding sizes. Then you go on to state that you would not expect a cooker installer to know how to.

So so if you don't expect them to know how to verify earthing and bonding then why are you expecting them to do so?
 
I could easily quote from a GN etc, but those publications are intended for a competent person.
Perhaps I should teach them all the adiabatic calculation?

Perhaps you should yes. If they are not competent to do their job, then why are they carrying out testing of circuits and installation of appliances ?
 
City and Guilds 2359 Level 2 qualification in Installing Consumer Electrical Equipment, full CCN1 and CKR1 Gas safe quals and internal training covering off electrical testing.

The guys are competent in their field, but are not electricians.
 
What do they learn on this course?

Who has decided they need to ensure bonding is the correct size and in place?

Diilb, their training is very comprehensive, but limited too.
We were challanged by NICEIC on not checking reg 132.16, my argument was we are not altering the installation, just connecting to it (after checking load etc) But NICEIC want us to just confirm presence of earthing conductors and main earthing conductors and confirm sizing is correct.
 
City and Guilds 2359 Level 2 qualification in Installing Consumer Electrical Equipment, full CCN1 and CKR1 Gas safe quals and internal training covering off electrical testing.

2359 is Servicing Equipment. No Electrical Installation training/quals then?
http://cdn.cityandguilds.com/Produc...ments/2359_L2_3_Qualification_handbook_v1.pdf

The guys are competent in their field, but are not electricians.

What, plugging things in :smilielol5:
 
Diilb, their training is very comprehensive, but limited too.
We were challanged by NICEIC on not checking reg 132.16, my argument was we are not altering the installation, just connecting to it (after checking load etc) But NICEIC want us to just confirm presence of earthing conductors and main earthing conductors and confirm sizing is correct.

Then you have three choices:
  • Train your staff properly to do their job in line with the requests
  • Perform on site pre-job assessments yourself or by similarly trained individual in line with requests
  • Tell the NICEIC that your work does not fall within the remit of their requests and to go forth and pester someone else.
 
Diilb, their training is very comprehensive, but limited too.
We were challanged by NICEIC on not checking reg 132.16, my argument was we are not altering the installation, just connecting to it (after checking load etc) But NICEIC want us to just confirm presence of earthing conductors and main earthing conductors and confirm sizing is correct.
Are you, or is your company part of a Competent Persons Scheme (NICEIC being one of them)
 
Then what business is it of NICEIC to tell you what to do?

Fair comment Pete!

It's because in the longer term we are looking at full scope for the whole business, so we need to be seen to be doing things correctly.

IMO, I don't feel we need to be doing any more than just a visual check that the incoming services are bonded, after all we are just installing appliances and do perform an EFLI test which will prove there is a 'decent' earth path. But their Area Engineer suggested we should be doing full 132.16 checks.
 

Reply to Earth and bonding cable checks-any tools available? in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

Disclaimer: I'm not going to attempt this job myself, I want a professional to do this job properly since I consider it non-trivial and need it...
Replies
2
Views
998
evening everyone . Quick question here I’ve recently took over a job that a friend of mine first fixed it’s a 3 bed semi house rewire. I don’t...
Replies
10
Views
2K
Hello All. I'm quite new to this game and gaining experience, but going well in the main. My customer wants to feed a Hob ( on island in centre...
Replies
5
Views
291
I'd appreciate a quick sanity check, thanks in advance: New circuit for a 3 phase cooker, in a community centre (run by a charity). Total load...
Replies
2
Views
1K
My Dad was a self employed electrician for 50 odd years. He sadly passed away in November and we have so much electrical & pluming stuff we don't...
Replies
18
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock