Hi all,

I am current doing an EICR on a commercial property and the original lights for the building are 4ft twin fluorescent with the nice diffuser with in built emergency lights.

At some point the emergency part of the lights has stopped working and someone instead of replacing the fitting or internals they have installed the emergency bulkhead next to the original fitting.

Now the question. None of the original fittings have had the battery's disconnected.

I've coded it C2 as risk of fire due to the battery's not holding a charge and not required.

Thoughts?
 
Are they actually still on charge?
 
Yes still all connected by when the power is off they don't work
 
How are the bulkheads connected, I doubt it is a huge issue but the emergency side should be disconnected and rerouted to the bulkheads.
 
All they have done is just wired the perm live, neutral and earth through the side of the old fitting into the bulkheads.
I have been told EICR only no works. I just feel if a battery that is not working is still connected there is a risk.
 
All they have done is just wired the perm live, neutral and earth through the side of the old fitting into the bulkheads.
I have been told EICR only no works. I just feel if a battery that is not working is still connected there is a risk.

The likelihood is that either the batteries are no good or there is a fault with the circuitry.

How is there a risk of fire ?
 
Speak to the client to disconnect the EM side of the fittings or replace to standard 4ft leaving bulkheads in situ.
 
That's what I'm doing recommending the em side is disconnected. I would say C2 due to the risk of the faulty batteries charging constantly. Maybe C3 just say it's noted
 
That's what I'm doing recommending the em side is disconnected. I would say C2 due to the risk of the faulty batteries charging constantly. Maybe C3 just say it's noted
You don't know if the batteries are faulty or if it's the circuitry, all you know is that the lights won't work as emergency lighting.

I can't see how it would warrant a C2.
 
  • Like
  • Agree
Reactions: UNG and westward10
Your right and I put it as a C3. I was over thinking it as a possible over heating problem but the fittings are designed for it.
 
  • Like
Reactions: mainline

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Joined
Location
Portsmouth
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
Practising Electrician (Qualified - Domestic or Commercial etc)
Business Name
BOSKS

Thread Information

Title
EICR code or not? Emergency lighting
Prefix
N/A
Forum
Periodic Inspection Reporting & Certification
Start date
Last reply date
Replies
9

Thread Tags

Advert

Thread statistics

Created
Boskselectrician,
Last reply from
Boskselectrician,
Replies
9
Views
285

Advert