Reaction score
230
I'm writing up an EICR. On one of the lighting circuits the potential load is theoretically about 1300W on a 5A BS3871 breaker. In reality, the arrangement has been in place for at least 8 years there are no signs of thermal damage, it is difficult to find lamps these days that would max out all of the fittings (although there are those vintage and tough lamps that get around this), and they are highly unlikely to ever have all of the lamps on at once. My instinct is to give it a code 3, what would you give it?
 
Last edited:
I'm writing up an EICR. On one of the lighting circuits the potential load is theoretically about 1300W on a 5A BS3871 breaker. In reality, the arrangement has been in place for at least 8 years there are no signs of thermal damage, it is difficult to find lamps these days that would max out all of the fittings (although there are those vintage and tough lamps that get around this), and they are highly unlikely to ever have all of the lamps on at once. My instinct is to give it a code 3, what would you give it?

why c3? if all tests are fine i cant see the problem.
 
My thinking is that when you design a lighting circuit you are supposed to do so taking into account the max wattage of the fittings being used e.g. Ib must be less than or equal to In which must be less than or equal to Iz. The I2 of the curcuit breaker will be above In and almost definitely above the potential load (so would not trip) and the manufacturer is unlikely to be in favour of the circuit breaker being subject to a level of current above the device rating under normal operating conditions (it may lead to overheating and shorten the life of the device).
 
Would you consider your circuit does not comply to reg 559.5.1.204?

No, the lampholders are still protected from overcurrent by a device that complies with that reg (provided the 5A MCB continues to work). It's the impact of up to 5.65A hypothetically running through a 5A MCB that I was wondering about. Perhaps I just need to apply a bit of engineering judgement and conclude that due to the current ban on regular incandescent lamps and diversity its not worth giving this a code...
 
If the potential load is theoretically 1300W then what is the actual, non theoretical load at the time you carried out the inspection?
Did you apply any diversity to the load or just count the number of lights?
What sort of environment is this in? What are the lights and how are they controlled?
If it's an office with 1300W of lights which is all switched on at once and stay on for the whole day then it's different to the lights in a house.
 
I haven't got my OSG on me but I believe that the guide recommends a maximum of 10 lights on a domestic circuit, is this a domestic circuit? And remember your test to the 7671 not a guide.

I can see where your coming from, but remember your protection device is really protecting the cable, not how many lights you have on a circuit. If you have a 1.0mm/1.5mm cable then unless it is seriously degraded by rating factors it will quite happily run on that 5 amp MCB.

Also remember you can have unlimited sockets on a RFC under 90m2 and you theoretically can plug 30 3 kw fires into it, but the PD will soon trip.

It is the same as your lights. You can have as many lights as you like on your circuit but eventually you will overload it and that 5 amp MCB will trip before there is damage to the cable.

For me it would be no code
 

Reply to EICR code - potential load on lighting circuit more than MCB rating in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

I am looking at installation of an architectural dimmer, that is will supply 6 channels, with 20A circuits each (2400W ea). Our hall has can light...
Replies
2
Views
683
My wife is on the committee of the local village, and they have just had an EICR carried out. This came out as 'unsatisfactory' and accompanied by...
Replies
14
Views
3K
Hi, recently carried out an eicr at a rented property. There were 5x 1mm in a 6amp mcb for lighting.. my question is what code should I be looking...
Replies
39
Views
5K
radiohead
R
I know how I was taught to test a RCD, 6 tests in all two no go, two under 300 mS and 2 under 40 mS with no load. But thinking about it not so...
Replies
7
Views
3K
I have a 230 Volt single-phase circuit with a 100 Amp cutout fuse and a 100 Amp MCB switch, so the supply is rated at 23 kVA. Only about 13% of...
Replies
54
Views
6K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock