I'll throw my hat in the ring on this one.

You are the man on the ground, so only you can make a sound judgement, so i won't agree/disagree with anything you have written.

This is what GN3 says about it.

C1, Danger present now. These must be brought to the attention of the responsible person/user/client etc immediately, and isolation and/or rectification is the be RECOMMENDED without delay.

C2, Is not dangerous at the present time, but if left unattended, it will become a C1 sooner rather than later, and rectification is advised ASAP.

C3, This is only to be used where improvement is advised or recommended.

C1 or C2, cannot and should not be used just because the installation does not meet the current version of BS7671.

The example i use is RCD's. If the install has no RCD's, and it wasn't a requirement at the time the install was first commissioned, then there is no obligation to fit them now. If the installation met the standards required when it was first installed, it was safe then, and if the only thing wrong with it now, is that it doesn't comply with current regs, then there is nothing wrong with it, and it remains safe for continued use. You can only ADVISE improvement for things like installation of RCD's and use the code C3.

It is well explained in both BS7671, and GN3. You can't force change or opinions onto people. I am not trying to imply that you or anyone else is trying to do this, but when using these codings, they need to be fully understood, as we are giving an expert engineering view of the installation, so we need to adopt giving expert advice to keep the trade professional.

Cheers………….Howard

I do agree with this, I think he RCD issue is something that's always going to be up for debate. I generally feel pretty happy about my codings but there will be the odd thing that throws a spanner in the works.

There always going to be an element of user interpretation, so long as the more real dangers C1 are noted, that's more important than saying you have no RCD on your hedge trimmer, but equally all results hold be recorded with as higher degree of accuracy as possible with the knowledge and understanding available to the person doing the inspection.
 
Can't one of you very experienced electricians here, publish a comprehensive of example of code infractions?? It seems that the majority of threads on this forum relate to ''What code for this and what code for that'' Obviously the official type code guides, are woefully inadequate or anywhere near comprehensive enough.
Sometimes i wonder if those conducting these EICR's should actually be taking this sort of work on.
 
  • Like
Reactions: 1 person
Can't one of you very experienced electricians here, publish a comprehensive of example of code infractions?? It seems that the majority of threads on this forum relate to ''What code for this and what code for that'' Obviously the official type code guides, are woefully inadequate or anywhere near comprehensive enough.
Sometimes i wonder if those conducting these EICR's should actually be taking this sort of work on.

That's a good idea, there could be a book with every possible situation in and what code to give it, that way it would be clean cut and no argument as it says it in the book, ideally some kind of official book.
 
Hi,


C2...Dead short on three out of five circuits between live and neutral, this is a potential fire hazard

How is this one possible, surely if they are "dead shorts" the protective devices have operated. Is it possible loads have been left connected?
 
  • Like
Reactions: 1 person
How is this one possible, surely if they are "dead shorts" the protective devices have operated. Is it possible loads have been left connected?
Very good point, to add if it is a dead short then the circuit cannot be energised surely so how can it be a fire hazard lol
 
Well, the house was not that big and I went through very room and fitting, nothing was plugged in at all, no loads anywhere...

Any ideas then? It was giving me 0.00 on IR between phase and neutral on three of the circuits. Honestly, there was nothing connected at all, no bathroom fans or humidity things, no appliances on anywhere...

- - - Updated - - -

I accept what you are saying, but if there were no loads, can you explain it?
 

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
EICR Codings
Prefix
N/A
Forum
Periodic Inspection Reporting & Certification
Start date
Last reply date
Replies
25

Advert

Thread statistics

Created
uksparks,
Last reply from
uksparks,
Replies
25
Views
9,771

Advert