Discuss EICR What would you do? in the UK Electrical Forum area at ElectriciansForums.net
the main points
I'll elaborate - I have been asked to remove showers, replace luminaires and install additional luminaries. I have had a quick look at the installation and I'm going offer, in the first instance, an EICR and recommendations with an estimate - I knew, from the start, that I was going to refuse the job if the client did not agree to a minimum of unifying the MCBs.
I just thought I'd get some interesting opinions and have. Thanks to all who replied - although maybe not Teletrix as I struggle to like Nirvana!
Well after wasting my time reading through this diatribe I’ve come to the conclusion the OP shouldn’t be doing EICR’s.
To write what is essentially a technical report on anything, you have to know what you are doing and not resort to asking random guy’s on the internet how to classify something. You should know!
Another observation, personal preferences are not a basis on which elements of the report should be written.
Aren't manufacturers allowed to assign the pre-assembled CU with some fairytale PFC rating as long as it's a complete unit? As soon as non-identical components are used this optimistic PFC rating would no longer apply.
Yes Marvo, that is the gist of it.
For compliance with annexe ZA of BS EN 60439-3, the CU MUST meet manufacturers requirements.
Fit an MCB by A.N. Other manufacturer, then it no longer meets that.
So it is the installers responsibility under law to ensure that the modified unit complies.
So C2, no option, end of.
Unless, the design calculations and test data for the modifications are available.
If you ignore this, just make sure that IF things go wrong, you can CYA, & your insurance is up to it.
Reply to EICR What would you do? in the UK Electrical Forum area at ElectriciansForums.net
On a Eicr on agreed limations of iinpections what do you normally put And what percentage do you test at..
Hi all. Just trying to get a feel for what everyone is charging for a commercial or industrial EICR with or without the previous report. Seems to...
Trying to organise a CU replacement at home. It's a 1930s property. It's got a 10way CU but with no RCD protection. Was after a larger unit with...
4K
Hello, I had an eicr done in 2021and it passed with four C3 items. They recommend next test date to be in 3 years instead of 5 on the certificate...
Hi everybody, I've been asked to do a EICR in a commercial property, So i popped in to have a look on my way home quickly and found the lighting...