Hi all,

First post here so go steady.

Recently installed a small radial circuit in my garage with 2.5, took it from a B16 breaker run through 20mm conduit on a wall. Tested everything with my megger with everything testing ok, happy days.

Couple of days later fired up my nail gun, on the 4th nail (roughly), it trips the 16A MCB. I know the nail gun will have a quick inrush of current as its a quick firing, so do you think changing it from a B type to a C type is a good option?

Perhaps upgrading it to a C20? Any advice would be appreciated

Cheers
 
I would try a Type C. I assume the circuit has additional rcd protection so fault protection is also provided if necessary, do you know the Zs at the socket outlet.
 
Hi - if you’ve the patience for an experiment - I’d try using it via a long extension lead. The lead will add some series resistance which may reduce the initial current surge enough to stop the mcb tripping.
 
if the Ze is nice and low, achieving an acceptable Zs for a 16A type C should be a doddle (about 1.44 ohms before correction/s).
 
you're just in with the Zs if you allow for temperature correction. x0. 8, if your cable ever gets up to 70deg. which is as likely as me refusing a beer.
 
Just musing, might you want to run more things at same time in future, possibly a heater in winter or extractor/vacuum?
Given conduit is already there by the sound of it I wondered if putting in 4mm singles on a B32 might be another idea to take the pressure off a bit (though from memory Zs would be right on the limit at 80%.)
 
Just musing, might you want to run more things at same time in future, possibly a heater in winter or extractor/vacuum?
Given conduit is already there by the sound of it I wondered if putting in 4mm singles on a B32 might be another idea to take the pressure off a bit (though from memory Zs would be right on the limit at 80%.)
Yeah I did think of this and suggested this to him, but he assured me he only uses small power tools in there very rarely. The most being a little palm sander and what not. Most of the time a radio at most. Thought 4mm may be a bit overkill but hindsight and all that
 

Reply to Electric nail gun tripping in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Called out to fault on RCD tripping maybe twice in a month for sometime. Did all the tests & found RCD was faulty, Refitted a new Rcd Type A which...
Replies
2
Views
795
Hey all, I'm looking for some advice to help me troubleshoot my strange issue with my consumer unit/fuse board on which my RCD keeps tripping...
Replies
25
Views
2K
Opinions on this Crabtree TP 10 way board? Got to test this next week after a quick recce on a clients site yesterday. Although probably...
Replies
12
Views
1K
Good evening, I have recently moved into a new home and I am having problems with the MCB/RCD tripping (Mem M6 Type 3 - 30mA). It intermittently...
Replies
8
Views
1K
Hello, I have an old 16A Wylex SK type B plug-in breaker in the fuse box in my garage which keeps tripping, and every time (and only at that time)...
Replies
5
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock