HappyHippyDad

-
Esteemed
Arms
Reaction score
5,578
At some point I'm going to get asked to fit one of the above and I'd like to know a bit more about it from some people that have already fitted them.

I've had a look through section 722, am I right in thinking the following:

1. Has to be on a dedicated circuit?
2. Has to have Type A RCD protection.
3. PME cannot be used if the charging point is located outdoors, therefore has to be TT'd?

Are the charging points that you can buy universal for every electric car or do you have to fit one that is suited to the customers specific car?

Any recommendations for charging points?

Cheers :)
 
At some point I'm going to get asked to fit one of the above and I'd like to know a bit more about it from some people that have already fitted them.

I've had a look through section 722, am I right in thinking the following:

1. Has to be on a dedicated circuit?
2. Has to have Type A RCD protection.
3. PME cannot be used if the charging point is located outdoors, therefore has to be TT'd?

Are the charging points that you can buy universal for every electric car or do you have to fit one that is suited to the customers specific car?

Any recommendations for charging points?

Cheers :)
My advice is to either invest in GN7 or the IET guide to electrical vehicle charging units for further guidance other than section 722
 
Dedicated circuit yes when looking at single chargers in domestic or workplace settings(however you can have more than 1 charger on them when there is software to balance load etc across the chargers and no overload circuit).
Some chargers have integrated type a rcd protection so dont need to put it at the cu but others such as the ev:box elvi units need upfront type a rcd protection as the dc monitoring stuff inside isnt compliant in the uk. I use rolec type a rcbos as they are only £20 a pop.
Cant use pme for a charger outdoors. cant really use tns either as the dno wont commit to saying they wont upgrade in the near future. so always assume it will be pme.

all new uk evs should now be on a type 2 plug rather than the older type 1. with tethered chargers you can usually replace just the lead if the car changes. teslas are a bit different.

Worth knowing that the renault zoe electric car does a loop check and if the Zs/Ra is too high it wont charge. not sure of the figure but its quite low so when on a rod it often stops charging if say ground dries out... customers go a bit mad when they find out. it isnt always posible to get a sufficiently low enough reading from even 2 rods so Renault pulled a cracker on this one.
 
Dedicated circuit yes when looking at single chargers in domestic or workplace settings(however you can have more than 1 charger on them when there is software to balance load etc across the chargers and no overload circuit).
Some chargers have integrated type a rcd protection so dont need to put it at the cu but others such as the ev:box elvi units need upfront type a rcd protection as the dc monitoring stuff inside isnt compliant in the uk. I use rolec type a rcbos as they are only £20 a pop.
Cant use pme for a charger outdoors. cant really use tns either as the dno wont commit to saying they wont upgrade in the near future. so always assume it will be pme.

all new uk evs should now be on a type 2 plug rather than the older type 1. with tethered chargers you can usually replace just the lead if the car changes. teslas are a bit different.

Worth knowing that the renault zoe electric car does a loop check and if the Zs/Ra is too high it wont charge. not sure of the figure but its quite low so when on a rod it often stops charging if say ground dries out... customers go a bit mad when they find out. it isnt always posible to get a sufficiently low enough reading from even 2 rods so Renault pulled a cracker on this one.
Does the Renault Zoe onboard Efli testing equipment need calibration every year? Just a thought!
 
I have been looking into this myself.

Im doing the C&G 2919-01 2day course next week which is required to register with OLEV.

Ill let you know how it goes.
Please do let me know how it goes Brendon, I'd be very interested.
How much does it cost?
 
I can’t seem to find a recent thread on car charging/PME supply, which had all the discussion about PME supply, so resurfaced this one (bet someone will find it now).

What makes of charges use a system that completely isolates the car from the supply?

Neighbours just got an electric car. So wanna be a smart arse before he has the charger installed.
[automerge]1582652298[/automerge]
I’ve just googled the vehicle. £72,000. Doesn’t include the charger, nor a sunroof. Perhaps it’s got PV on the roof?
 
Last edited:
At some point I'm going to get asked to fit one of the above and I'd like to know a bit more about it from some people that have already fitted them.

I've had a look through section 722, am I right in thinking the following:

1. Has to be on a dedicated circuit?
2. Has to have Type A RCD protection.
3. PME cannot be used if the charging point is located outdoors, therefore has to be TT'd?

Are the charging points that you can buy universal for every electric car or do you have to fit one that is suited to the customers specific car?

Any recommendations for charging points?

Cheers :)
As I am a tutor of EV charge points the correct answers are:
1.
[automerge]1585488167[/automerge]
As I am a tutor of EV charge points the correct answers are:
1. It is best to be a dedicated circuit so as not to make it a more difficult installation.
2. Yes you are right it must have a type "A" rcd.
3. If the charge point is in a garage that is attached to the building it does not need to be "tt'D" if it is not attached it then needs to be made into a "TT" system. The earthing is more detailed but I would need to know the installation in more detail.

Regards

[email protected]
 
Last edited:
As I am a tutor of EV charge points the correct answers are:
1.
[automerge]1585488167[/automerge]
Did you mean to write more rather than just '1'?
I think possibly a tutor would have written an explanation for each of the 3 questions, not just written '1'. :D
 
Did you mean to write more rather than just '1'?
I think possibly a tutor would have written an explanation for each of the 3 questions, not just written '1'. :D
read the next bit
[automerge]1585490793[/automerge]
Think his reply is within the 'quote box', and I'm no expert but I don't agree with his answer for 3.
yes your are right you are not an expert or even picking up that more information is required to give accurate and correct information.
 
read the next bit
[automerge]1585490793[/automerge]

yes your are right you are not an expert or even picking up that more information is required to give accurate and correct information.

Thats a bit harsh?

You said;

'If the charge point is in a garage that is attached to the building it does not need to be "tt'D" if it is not attached it then needs to be made into a "TT" system''.

Thats, if I recall, is not what is exactly said in Section 722.
 
read the next bit
[automerge]1585490793[/automerge]

yes your are right you are not an expert or even picking up that more information is required to give accurate and correct information.
When I was teaching Maths many moons ago I don't think I would have ever responded to a pupil like that. It would not have aided in their learning, it would just embarrass them and stop them from asking questions again.
Ps. Thankyou for taking the time to offer suggestions to my questions though.
 
My take on the answers are
1. Has to be on a dedicated circuit?

Not mandatory, but makes sense much more than any general circuit

2. Has to have Type A RCD protection.

Sort of! The output must be protected by type A - PLUS 6mA DC protection, (or type B as an alternative), often this is included within the charge point, so swa and mcb protection can be used on the supply to the charge point.


3. PME cannot be used if the charging point is located outdoors, therefore has to be TT'd?

In my opinion - yes, but the standards do allow the use of the pme earth if you utilise special devices to identify a lost pen/CNE; if these are within the charge point, then ok, although I don't believe they actually provide the protection needed for safety - but as the manufacturers have pressurised the committee to accept them, and it's in the spec (amd 1) then you could use them.
 
Last edited:
My neighbour had his car charger fitted this week (PME supply). As far as my nosey neighbour goggles tell me, there's no obvious signs of a rod. Can't quite make out the make of the box of tricks, but the stress is getting to me. Might just ask him outright. :)
 
Thats a bit harsh?

You said;

'If the charge point is in a garage that is attached to the building it does not need to be "tt'D" if it is not attached it then needs to be made into a "TT" system''.

Thats, if I recall, is not what is exactly said in Section 722.
The 18th Edition amendment does say this. When i delivered the course 2 weeks ago this was discussed at length because when it is made into a "TT" system the swa if it is used, will have the armouring earthed at the domestic consumer unit but not attached as an earth at the EV charge unit. You then use the earth rod, if you are using one for an earth, for the EV charge point system in the garage. Also it must not be possible to simultaneously touch the house extraneous conductive parts and those of the garage as if they are at a different potential we all know what could happen.
[automerge]1585500698[/automerge]
I can’t seem to find a recent thread on car charging/PME supply, which had all the discussion about PME supply, so resurfaced this one (bet someone will find it now).

What makes of charges use a system that completely isolates the car from the supply?

Neighbours just got an electric car. So wanna be a smart arse before he has the charger installed.
[automerge]1582652298[/automerge]
I’ve just googled the vehicle. £72,000. Doesn’t include the charger, nor a sunroof. Perhaps it’s got PV on the roof?
Isolation from the supply can be achieved by using an isolation transformer. But it is still fed from the house originally. Or a PV array but the charging will take a lot longer.
[automerge]1585500827[/automerge]
When I was teaching Maths many moons ago I don't think I would have ever responded to a pupil like that. It would not have aided in their learning, it would just embarrass them and stop them from asking questions again.
Ps. Thankyou for taking the time to offer suggestions to my questions though.
no problem
 
Last edited:
The 18th Edition amendment does say this. When i delivered the course 2 weeks ago this was discussed at length because when it is made into a "TT" system the swa if it is used, will have the armouring earthed at the domestic consumer unit but not attached as an earth at the EV charge unit. You then use the earth rod, if you are using one for an earth, for the EV charge point system in the garage. Also it must not be possible to simultaneously touch the house extraneous conductive parts and those of the garage as if they are at a different potential we all know what could happen.
[automerge]1585500698[/automerge]

Isolation from the supply can be achieved by using an isolation transformer. But it is still fed from the house originally. Or a PV array but the charging will take a lot longer.
[automerge]1585500827[/automerge]

no problem
But it does not mention ‘an attached garage’ or ‘not attached’.

It says (paraphrasing slightly),

‘PME earthing facility shall not be used as the means of earthing for the protective conductor contact of a car charging point located outdoors or that might be reasonably expected to be used to charge a vehicle located outdoors, unless one of the following methods is used;’ (722.411.4.1)

A subtle difference, do you not agree?

I‘ve not seen an isolating transformer for a car charger just yet.
 
Last edited:

Reply to Electrical car charging point installation in the Electric Vehicles Advice Forum area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock