I came across this today when changing a shower isolator that was stuck in the on postition.

40A Hager RCBO feeding 10mm² twin + earth to a pull cord shower isolator. On the load side of the isolator there was 10mm² going off to the shower as you would expect, but also from the isolator was 2.5mm² T+E feeding a 3A fused spur in the loft, which then fed an extractor via 1.5mm² T+E.

So the extractor is switched on and off with the isolator, along with power to the shower. Not very good practice IMO, but is it compliant?

I believe so: the 2.5mm² and 1.5mm² T+E should be protected from overload by the 3A fuse. PFC was about 1100A, so the requirements of the adiabatic equation should be met. RCD protection means disconnection times are met.

What do you guys and girls think?
 
My biggest concern is that the fused spur is in the loft and may not be accessible.
 
Switches and protective devices should be accessible.
Partly for safety to turn off in emergency
Mainly for convenience though.
 
Don't see an issue really, just a bit unusual, I have come across this before, my own house has underfloor heating in an en-suite shower that is fcu'd off the shower itself.

Got busy with my calculator when I found out, everything was ok disconnection times, adiabatics etc

There is the issue of circuits not being as independent as I would have liked, but other than that...
 
I hadn't considered that. Actually one of the better lofts I've been in - loft ladder, boarded out, and with a light. But you think it would be a reg breaker had it been under 12" of itchy stuff?
The insulation is, nt an issue as both the 2.5 and 1.5 will never be carrying more than the fan load. The 3 amp fuse is well below what the regs allow for cables of those sizes embedded in insulation. In practice however it would be better to connect the fan to the light. I personally like to wire the fan back to the switch and allow the customer the option of switching the fan separately
 
The insulation is, nt an issue as both the 2.5 and 1.5 will never be carrying more than the fan load. The 3 amp fuse is well below what the regs allow for cables of those sizes embedded in insulation. In practice however it would be better to connect the fan to the light. I personally like to wire the fan back to the switch and allow the customer the option of switching the fan separately
They will under fault conditions prior to the spur.
 

Reply to Extractor fan from shower isolator in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

Hi Customer has an extractor fan that’s inside the shower cubicle high up on the wall. The extractor fan has no form of isolation and is wired...
Replies
8
Views
1K
I’m replacing an old 100mm extractor fan in the kitchen with a new one. The old one was a pull cord fan whereas I bought a timer one (no pull...
Replies
3
Views
400
Hi, I'm looking to install a new bathroom extractor fan in my bathroom as I have a windowless bathroom and the current one I have installed in...
Replies
13
Views
722
Hi all, I'm in the UK and have recently had a ducted extractor fan Mixflo 200W with timer fitted. The fan comes on with the pull cord and runs for...
Replies
6
Views
317
Good evening all, I’m currently part way through my apprenticeship and we are working on IB, IN, IZ and IT and volt drop today. And it got me...
Replies
4
Views
477

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock