Hi All

I have door entry system that i installed at a care home. it is a fail safe system but they didnt ask me to coonect to fire alarm system unitl after i had second fixed it all.

Long story short i have connected it (through a relay) to a local fire alarm sounder that gives out 24v on alarm conditions.
This works correctly but the fire panel shows a fault on the sounder system. Is there an easy fix? Maybe connecting a resistor? any help would be appreciated.

Thanks
 
I'm no expert on fire alarms systems by any means, but there are usually outputs on the panel PCB to connect to for things like this.
Someone will be able to set you right soon I reckon.
 
  • Like
Reactions: 1 person
Thanks for your reply.
The reason i have connected to a local sounder is that the fire panel is the other side of the building and not easily wired back from.
 
maybe a blocking diode would get you out of trouble. however, it's not recommended to modify any fire alarm system without thoroughly considering the implications of failure to operate in case of a fire.
 
  • Like
Reactions: 1 person
where's tazz when he's wanted.

51OpAgmoRUL._AA160_.jpg
 
maybe a blocking diode would get you out of trouble. however, it's not recommended to modify any fire alarm system without thoroughly considering the implications of failure to operate in case of a fire.

Is a blocking diode what normally comes with detector bases?
 
yep. it conducts d.c. one way with a 0.6 volt drop, but blocks the other way. the diode used is selected according to the current requirement. not sure if it will cure your problem though.
 
yep. it conducts d.c. one way with a 0.6 volt drop, but blocks the other way. the diode used is selected according to the current requirement. not sure if it will cure your problem though.

Thanks for your reply.

How would i connect that diode? across the positive and neg going to my relay or just on the positive out in series? and would it also stop the relay from operating?
 
personally i wouldnt be messing around with a fire alarm in an old folks home
well risky if something goes wrong
lnstall a stand alone sounder
 
As tel mentioned a diode will do the job, however it isn't the right way and will need to be a very temporary fix, Tazz where are you ??
 
Connecting any release or shutdown to the sounder circuit, is a breach of regs......reason being, the doors will relock when system is silenced....and must only relock when the system is fully reset. All release, shutdowns must be off panel fire relay, or addressable output unit.
Example, fire alarm activates in nursing home, doors release, then staff member silences system while evacuating...doors relock trapping residence in building
 
  • Like
Reactions: 2 people

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
Fire alarm sounder connected to door entry system help please
Prefix
N/A
Forum
Security Alarms, Door Entry and CCTV (Public)
Start date
Last reply date
Replies
15

Advert

Thread statistics

Created
Ross Harvey,
Last reply from
tazz,
Replies
15
Views
2,257

Advert