Evening all.
I am about to change a CU but have poor IR results on the ring so I am investigating that first.
N-E on the ring 'WAS' 0.1Mohm. I started narrowing it down and got to a wall mounted JB (it looked like a cooker outlet plate, it had 2 spurs as well as 2 cables for the ring). The spurs tested fine, the ring tested 1.1Mohm on one side and about 4Mohm on the other? When I reconnected the lines of the ring at the JB the N-E on the 'faulty' side went to 0.5Mohm. When I disconnected the lines in the JB the faulty side went back to 1.1Mohm?
I then continued to eliminate further sockets and when I went back to this JB the IR results were 0.3Mohm whether the lines were connected or not?
I have not been able to unplug everything as the homeowner is a hoarder to the extreme. I have narrowed it down to 5 sockets (or JB's hidden in floorboards). The cable is imperial.
I am going back soon and I have asked for access to the 5 suspect sockets but I am a bit confused as to varying IR results?
Plus... I got a bit carried away finding the poor IR results and at the end of the day found that the cpc on the ring is broken!
Cheers chaps... and sparky chick!
I am about to change a CU but have poor IR results on the ring so I am investigating that first.
N-E on the ring 'WAS' 0.1Mohm. I started narrowing it down and got to a wall mounted JB (it looked like a cooker outlet plate, it had 2 spurs as well as 2 cables for the ring). The spurs tested fine, the ring tested 1.1Mohm on one side and about 4Mohm on the other? When I reconnected the lines of the ring at the JB the N-E on the 'faulty' side went to 0.5Mohm. When I disconnected the lines in the JB the faulty side went back to 1.1Mohm?
I then continued to eliminate further sockets and when I went back to this JB the IR results were 0.3Mohm whether the lines were connected or not?
I have not been able to unplug everything as the homeowner is a hoarder to the extreme. I have narrowed it down to 5 sockets (or JB's hidden in floorboards). The cable is imperial.
I am going back soon and I have asked for access to the 5 suspect sockets but I am a bit confused as to varying IR results?
Plus... I got a bit carried away finding the poor IR results and at the end of the day found that the cpc on the ring is broken!