Hi,
I was wondering if anyone has come across this before. I was doing an insulation resistance test on a property practising for my periodic exam. I set the tester to 250v because I couldn't remove all equipment, when I went to test across the live conductors and CPC I didn't get a reading and the tester only 'ramped' up to 4v.
When I got home and tested it on my test rig the tester ramped up and took a reading as normal. Any ideas what could have caused this?
silly question but are you sure you isolated the circuit under test?
I'm pretty sure I isolated everything accordingly, I performed safe isolation and 'attempted' to perform a full board test. Would you recommend performing a test on individual circuits if this problem occurs.
Post the model of your fluke so some one with knowledge on the tester can reply.
If doing a insulation test the reading should be Meg ohms not volts so if it reads volts what is the tester picking up??
My tester will shut down and give a warning if voltage is detected and not alow you to test..
Hi,
It's a Fluke 1562. The tester is getting a reading of 0.00 Meg ohms and when I mention voltage the tester shows what it has 'ramped' up to. It should be ramping up to 250v as that is what I set it to, but it is only ramping up to 4v.
Any suggestions would be much appreciated! cheers,
Andy.
well the meter is quite clearly giving you a reading - a reading of 0.00 Mohms. I suggest there's a fault in the circuit somewhere.
what i do once a month is IR test a 1 Meg. resistor. then i know the meter is right.
Well no it's not because it's not testing at voltage. If it ramped up to 250v and I got 0.00M ohms then yes I'd agree, but the highest it got to was 4v.
Thanks, telectrix that's a good suggestion.
What has happened is that the tester can't apply the 250V because there is a low resistance between the test leads, I would suggest that whatever you can't remove is soaking up the energy the tester is trying to apply to the circuit, henmce the low voltage.
If the reading is between L-N then clearly something is on, if its between L-E then its getting to E through the neutral route - disconnect both L & N from the CU and try again.
Reply to Fluke Insulation Resistance No Reading in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net
Hello all, I hope you're all keeping well. I have a question regarding insulation resistance testing. Whether doing a single circuit IR test or...
I’ve recently come into a people’s with my fluke T130 I’ve been proving it recently on my fluke proving unit and it shows 60v then ramps up to 90v...
Electrical2Go - Megger MFT Deals! Upgrade your toolkit with our exclusive offer! Purchase any of the Megger advanced multifunction testers –...
I want to check the insulation of the 3-phase 400VAC asynchronous squirrel cage motor. Motor's stator windings are connected in delta. I've read...
Chaps - having problems with a new Megger MIT420/2 insulation/continuity tester 'oscillating' and failing to give stable resistance readings in...