acxman

Hi All,
I’m a retired electrician from the Detroit area. My question is, I need to replace some old two prong receptacles in my daughters 75 year old home. Code says I can install a GFCI receptacle in the first receptacle of a group of receptacles and install standard three prong receptacles downstream from the GFCI. But, in that scenario I have to locate the first receptacle. That can be difficult in these old homes.

What I would like your opinion on is can I just install a GFCI breaker, for that circuit, in the panel? Then I do not have to worry about which receptacle is first in the circuit?

Thanks
Tom
 
This is one for one of our USA members such as @Megawatt

Here in the UK the RCD (GFCI) is normally always in the panel so it also protects the fixed wiring against accidental nailing during DIY, etc.
 
  • Like
Reactions: Megawatt
Hi All,
I’m a retired electrician from the Detroit area. My question is, I need to replace some old two prong receptacles in my daughters 75 year old home. Code says I can install a GFCI receptacle in the first receptacle of a group of receptacles and install standard three prong receptacles downstream from the GFCI. But, in that scenario I have to locate the first receptacle. That can be difficult in these old homes.

What I would like your opinion on is can I just install a GFCI breaker, for that circuit, in the panel? Then I do not have to worry about which receptacle is first in the circuit?

Thanks
Tom
Yes that would be fine but they are expensive but there is one stipulation that you have to install stickers on the covers stating no equipment equipment on every receptacle and yes you can install the 3 prong covers.
 
Yes that would be fine but they are expensive but there is one stipulation that you have to install stickers on the covers stating no equipment equipment on every receptacle and yes you can install the 3 prong covers.
I have to agree with you that finding the first outlet on a circuit can be challenging in the older houses.
 
Megawatt, Thank you. I was pretty sure it would be the same as installing a GFCI in the first outlet, but just wanted to make sure. And, yes I still would have had to label the receptacles accordingly. Thanks for you quick reply.
 
Megawatt, Thank you. I was pretty sure it would be the same as installing a GFCI in the first outlet, but just wanted to make sure. And, yes I still would have had to label the receptacles accordingly. Thanks for you quick reply.
Your quite a my friend
 

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
GFCI circuit protection when replacing old non grounded receptacles
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
6

Advert

Thread statistics

Created
acxman,
Last reply from
Megawatt,
Replies
6
Views
1,124

Advert