Yes, but none of them fit a UK-style CU busbar arrangement do they?
We have never had problems getting DP RCBO as standard fitting for a caravan supply, the problem if finding RCBOs for a CU that are neutral switching, but thankfully now a few are (Wylex, Crabtree, Fusebox).
Doing away with flying leads and simply having a neutral busbar would be the answer, but that is not likely here for some time I suspect...
Is a neutral busbar worth the additional space required for 2 module RCBOs?
Would those Hagar RCBOs have any benefit over Crabtree, Wylex or Fusebox 1P+N single module RCBOs in a domestic application, other than flylead?
Yes the do, and use a 13mm pitch dual busbar: A9XPH224 | Schneider Electric Acti 9 2 Phase Busbar, 24 Module, 415V, 18mm Pitch | RS Components - https://uk.rs-online.com/web/p/busbars/7762724/
A wylex enclosure and main switch. Hager devices and Schneider bus bar!
Mixing and matching is not allowed here now.
As above, no major U.K. supplier has a CU with that sort of arrangement. Possibly SBS, but I’d rather use a manufacturer where parts will be more likely to be readily available long term and available locally on the shelf.
For the typical UK case where N is very much at a low potential to E by design and installation verification, then no.
They seem to bo common in the EU where they have TT as the norm and perhaps traditionally did not have N as near Earth potential. Either as historically it was more like a split-phase supply taking 2 of a 3-phase line set, or for whatever reason they demanded over-current protection on the N side.
The "neutral switching" 1P+N RCBO you see here will detect and isolate an earth fault that happens via the N side, but they do not detect over-current on that side as that is not a UK requirement going back a long, long way. Even when the 13A plug design was introduced in the 40s it was line-side fuse only as installations could be trusted to have N approx E in potential.
Reply to Global IR testing on RCBO populated CU in the UK Electrical Forum area at ElectriciansForums.net
Did a check on a ring circuit, due to board having to remain live I did it at a socket.. Was an RCBO, had checked RCD side and all tested ok...
Hi All New to this forum, have read the posts on here from google but only recently signed up. I'm having some issues and some input would be...
Doing some testing today on a Wet Room installation. Fed from its own small CU. And consists of 2 x seperate 50A (for 10.5kw shower) circuits...