For the typical UK case where N is very much at a low potential to E by design and installation verification, then no.

They seem to bo common in the EU where they have TT as the norm and perhaps traditionally did not have N as near Earth potential. Either as historically it was more like a split-phase supply taking 2 of a 3-phase line set, or for whatever reason they demanded over-current protection on the N side.

The "neutral switching" 1P+N RCBO you see here will detect and isolate an earth fault that happens via the N side, but they do not detect over-current on that side as that is not a UK requirement going back a long, long way. Even when the 13A plug design was introduced in the 40s it was line-side fuse only as installations could be trusted to have N approx E in potential.

Are those double module RCBOs providing over-current protection on N? The reason I ask is that Hagar market them as 1P+N, rather than DP, which is the same terminology used in the single module RCBOs we see.

I know my questions probably seem incredibly stupid, but it seemed like a good time to ask. What I'm driving at is whether or not 1P+N single modules would provide adequate protection in other European countries or if I'm missing something about their operation?
 
Are those double module RCBOs providing over-current protection on N? The reason I ask is that Hagar market them as 1P+N, rather than DP, which is the same terminology used in the single module RCBOs we see.
You are right, they are 1P+N even though Hager sometimes refer to them as 2P. Oddly enough the 4P ones appear to really be 4 protected paths for over-current:

I know my questions probably seem incredibly stupid, but it seemed like a good time to ask. What I'm driving at is whether or not 1P+N single modules would provide adequate protection in other European countries or if I'm missing something about their operation?
I don't know. You would need to check the local regs to see what is required.

My French is not up to decoding this to see if it really is 2P instead of 1P+N, and the picture is not quite good enough for me to see if the little printed schematic is showing the thermal/magnetic trip on both paths, but maybe someone on here can tell:
 
I have been told by the Electricity provider in France that the single module RCBO's do not comply, bit difficult to tie them down to why, but in essence I think they said because the isolation is not a 3mm air gap when tripped and the neutral only provides protection because it is dragged along with the tripping phase and does not have its own tripping mechanism.
 
In the case of ROI I would not be surprised if it was a mix of the single-pole OCPD based on the historic ties with the UK regs, and the move to double-pole switching from more recent EU influence and/or historical use of TT or similar, leading the 1P+N being normal for RCBO.

Might explain the difference in part number for the same basic module size between the Hager .ie and .fr sites.

Maybe @Risteard knows more on the background?
 
You are right, they are 1P+N even though Hager sometimes refer to them as 2P. Oddly enough the 4P ones appear to really be 4 protected paths for over-current:


I don't know. You would need to check the local regs to see what is required.

My French is not up to decoding this to see if it really is 2P instead of 1P+N, and the picture is not quite good enough for me to see if the little printed schematic is showing the thermal/magnetic trip on both paths, but maybe someone on here can tell:
Interesting on the Hager French web site posted above in the description is says "With neutral pole cut NO.
 
I have been told by the Electricity provider in France that the single module RCBO's do not comply, bit difficult to tie them down to why, but in essence I think they said because the isolation is not a 3mm air gap when tripped and the neutral only provides protection because it is dragged along with the tripping phase and does not have its own tripping mechanism.

There was a similar discussion which (I think) concluded that single module RCBOs did provide a 3mm air gap.

What I'm really curious about is why Hagar have designated these double module RCBOs 1P+N and not DP? The terminology suggests that N isolation operates in the same manner as single module units.

Edit: Just seen Mike's latest reply and the plot thickens!
 
My previous post was prompted by a visit from a French Consuel Inspector, so in essence it could just be his opinion, but certainly if the dual RCBO's do not have their own trip mechanism, why are they so big if the same can be made in a single module?
 
My previous post was prompted by a visit from a French Consuel Inspector, so in essence it could just be his opinion, but certainly if the dual RCBO's do not have their own trip mechanism, why are they so big if the same can be made in a single module?

Technology continues to improve. What I'm wondering is whether or not there is any practical purpose for continuing to use two modules if one would suffice? I'd always assumed double modules RCBOs provided true DP isolation, but that Hagar link prompted me to ask questions.

My knowledge is extremely limited, but my capacity for asking questions knows no bounds.
 
This should be clearer:
Imports - 1 of 1 (2).jpeg
 

Reply to Global IR testing on RCBO populated CU in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Did a check on a ring circuit, due to board having to remain live I did it at a socket.. Was an RCBO, had checked RCD side and all tested ok...
Replies
3
Views
1K
Hi All New to this forum, have read the posts on here from google but only recently signed up. I'm having some issues and some input would be...
Replies
13
Views
2K
Please advise what I should test / check next. My usual qualified electrician who did all of the work here is in Ireland for 4 weeks and not...
Replies
45
Views
3K
Doing some testing today on a Wet Room installation. Fed from its own small CU. And consists of 2 x seperate 50A (for 10.5kw shower) circuits...
Replies
23
Views
3K
I'm practising EICRs on friendly locations as I'm still in training - technically done my 2391-52 but frankly need loads more practise. I've just...
Replies
11
Views
917

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock