Okay, so, I’m currently working towards becoming an electrician and was after some guidance for a job that I’m working on.

The property (a small flat) has a few circuits on RCBOs.
1 Ring (kitchen)
1 Radial Sockets
1 Internal Lighting
1 External Lighting

The owner occupier is replacing their kitchen and is wanting grid switches as a means to isolate their appliances:

Fridge freezer
Igniter on gas hob
2kW oven
Washing machine

I’m looking at Click Minigrid.

There doesn’t seem to be any clear guidance on the grid switches be that from the manufacturer or otherwise.

The grid switches are 13A double pole. Now some say they need their own fuse, other say they don’t if the device they’re coming trolling has its own fuse such as a that found in a plug top, others say it needs to be a radial, other say it can be done off a ring.

I’m figuratively pulling my hair out.

So, for my question...

Can these grid switches be used on a ring main without the need for a fuse on the grid plate, if so, can someone show me and/or explain how they would be wired?

I’m thinking it would be:

Incoming supply to the grid switch (from ring main) feeds an unswitched socket from the ‘outgoing’ load on the grid switch. The fuse would be in the plug top on the appliance.

To continue the ring, this is looped in and out at the grid switches.

See Image (forgive the artwork)
edit here’s a link to the grid switches - https://www.electricalcounter.co.uk...P+Switch+Module,+'WASHING+MACHINE'/2454004957
 

Attachments

  • 47A0FD89-8220-43AA-9ECD-2D78404BCC4F.jpeg
    313.8 KB · Views: 38
Last edited:
I would be careful with that amount of load running through one area of the ring. Grids are notorious for tight cables, give yourself a deeper backbox if you can.

Your drawing is wrong, as it’s not a ring.

I would put the oven on its own radial, but mounted in the same grid, the ring looped through the other 3 switches.

Think of it as spurs coming from the ring from different positions, you don’t need to fuse down at each switch.
 
separate circuit to the grid switches, either a ring in 2.5mmor a radial in 4mm. (either way on a 32A MCB/RCBO). switches should be 20A D/P.
 
I would be careful with that amount of load running through one area of the ring. Grids are notorious for tight cables, give yourself a deeper backbox if you can.

Your drawing is wrong, as it’s not a ring.

I would put the oven on its own radial, but mounted in the same grid, the ring looped through the other 3 switches.

Think of it as spurs coming from the ring from different positions, you don’t need to fuse down at each switch.
Thanks.

I realised after I posted, I’d not drawn the outgoing leg of the ring.
 
I would be careful with that amount of load running through one area of the ring. Grids are notorious for tight cables, give yourself a deeper backbox if you can.

Your drawing is wrong, as it’s not a ring.

I would put the oven on its own radial, but mounted in the same grid, the ring looped through the other 3 switches.

Think of it as spurs coming from the ring from different positions, you don’t need to fuse down at each switch.
Thanks for the insight RE the back box and for the tip on the oven.

Am I correct in that I'd wire up everything as per my (new) picture for implementing the grid switches into a ring with incoming and outgoing legs looping between the supply side of the switches?

Where you say that the oven should ideally be run off its own radial. I'm guessing I'd run it through the 'oven' switch on the grid as I would with any ordinary cooker switch? As it's only 2kW, could this not be run off a 20A RCBO with 2.5mm T&E?

I'd be grateful for any insight.

I've added two images that I've drawn this morning, if someone could clarify if this is the correct way to wire the switches as a ring (looping in and out of the switches and treating the loads as spurs) and the second image which omits the oven from the ring and has this as its own radial.

Thanks so much in advance.
 

Attachments

  • grid-switches.png
    7.2 KB · Views: 67
  • grid-switch-with-radial.png
    11.6 KB · Views: 59
I see you are a trainee so is this a private job or something you are undertaking for your employer.
 
separate circuit to the grid switches, either a ring in 2.5mmor a radial in 4mm. (either way on a 32A MCB/RCBO). switches should be 20A D/P.
Thanks.

Any reason I’d need 20A rather than 13A when the load on each is less than 13A?

am I correct in saying you would leave kitchen sockets on their own ring and have the grid switches on a new ring circuit?
 
Thanks.

Any reason I’d need 20A rather than 13A when the load on each is less than 13A?

am I correct in saying you would leave kitchen sockets on their own ring and have the grid switches on a new ring circuit?
Because dp switches come rated at 20A....

The grid can be part of the same ring as the kitchen, but be aware of high power items that could overload the circuit if all on at the same time.

The oven is the highest draw that I can see. Put it on its own radial.
 
Any 'fixed' appliance 2kW or over (in this example, the oven), should have its own dedicated supply from the CU.
Igniter and fridge/freezer are trivial loads, and wash/mac. is a high, but very intermittent load, so these three could come off of the existing RFC. They will need fusing downstream from the switches.
 
In most cases the grid switches will be feeding an unswitched 13A socket, or maybe a FCU, so you have your <= 13A fuse there.

But definitely a deep back-box!
 
This is a private job that is then going to be tested and signed off. Any reason?
Nothing personal on you @daavvee , just due diligence, and probably a polite advert (to follow) to join our trainees section in a slightly 'less hostile' area of the forum.

The difference between how public doing thier own electrics and trainees doing electrics is the whole 'a little knowledge can be dangerous' thing, the trainee section allows the seeking of advice and better steering towards an outcome, with a bit of creative feedback in the process, plus there are others in your position too ?
 
Because dp switches come rated at 20A....
Indeed. However, the data sheet for Click Mini Grid Double Pole single module switches says they are 13 amp (resistive) ,10AX.
This is not something I've come across before.
Could be confusing for the less experienced.
I would be inclined to (not install appliances on a grid system, just my personal preference) install a proper grid switch system with the DP switches rated at 20 amps.
 
I only used the click minigrid once for kitchen appliance switching and had a few issues with it so I wouldn't recommend it. When I was chatting to one of the Scolmore reps about the problems I had they recommended using the grid pro range instead
 
Some grid switches are intended for lighting and 10A or so rated, others are 20A, typically the DP switches, so you do need to check the spec carefully!
The Click Mode Mini Grid DP 13 amp rated switches come labelled with appliances like Oven, Washing Machine etc.
Although I'm a big fan of the Click range in general, I am a little skeptical about the use of the Mini Grid switches for high load appliances.
 
The Click Mode Mini Grid DP 13 amp rated switches come labelled with appliances like Oven, Washing Machine etc.
Although I'm a big fan of the Click range in general, I am a little skeptical about the use of the Mini Grid switches for high load appliances.
Part of the problem I had was the stiffness of the 2.5 cable was twisting the switches out of the grid as you pushed it back into the box with similar problems if you need to remove it to replace a switch IMO using the minigrid created more problems than it solved
 
So I spoke with Scolmore directly today, who I might add, were extremely helpful.

They’ve said that the grid switches can form part of a ring protected by a 32A MCB/RCBO and that the grid switches do not need to be fused providing the appliance that is connected has its own fuse. Moreover, they have said that the 13A grid switches would be suitable fo everything, but did mention a deep back box and perhaps a radial for any high demand appliances.

Kudos to all those who helped.

First fix complete. Let’s see how things go.
 
Any 'fixed' appliance 2kW or over (in this example, the oven), should have its own dedicated supply from the CU.
Igniter and fridge/freezer are trivial loads, and wash/mac. is a high, but very intermittent load, so these three could come off of the existing RFC. They will need fusing downstream from the switches.
I should I expanded more on the last sentence. Fusing is required, but this can be the fuse in a 13A plug, if the switch is connected to a single 13A socket, or a fuse in a SFC if the appliance is hard wired.
I would not include a fuse built into an appliance, because the appliance might be replaced by unfused version, by an unskilled person, at some time in the future.
 

Reply to Grid / Minigrid wiring to an unswitched socket for kitchen appliances. in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hello everyone, I'd like to seek your input on a matter. I'm in the process of designing the electrical connections for the following kitchen...
Replies
38
Views
3K
Hello Electrical world. Looking for thoughts and opinions. Currently planning out my kitchen re-wire for new kitchen. I was originally...
Replies
13
Views
3K
I'll start by saying - I have absolutely no intention of doing any wiring or anything electrical myself. You get someone professional to do a...
Replies
8
Views
784
HI All, I am building a new house (self build) and have my part P so am running the cabling. My reading of the regs says that any appliance of...
Replies
18
Views
4K
Hi everybody, Looking at putting a kitchen grid switch in my kitchen and wanted to see what you guys (and girls) thoughts were about my set up as...
Replies
9
Views
7K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.