Hi
Needing help with a PIR.

1. Old wylex type 2 CBs what BS is this an what Ka rating does it have.
2. MEM Memway 3 phase DB with rewireable fuses i take it they are a BS3036
3.The Memway is fed via an 60A TPN switch fuse Oterail make would this have a BS No
4. Method of protection on PIR is this Automatic Disconnection of Supply.

Anyway thanks in advance for any help
 
Hi
Needing help with a PIR.

1. Old wylex type 2 CBs what BS is this an what Ka rating does it have.
2. MEM Memway 3 phase DB with rewireable fuses i take it they are a BS3036
3.The Memway is fed via an 60A TPN switch fuse Oterail make would this have a BS No
4. Method of protection on PIR is this Automatic Disconnection of Supply.

Anyway thanks in advance for any help

1. Bs3871 normally 6Ka

2. Yes 3036

3. Could be bs60947-3

4. On a PIR pre 17th its EEBADS
 
1. More than likely BS 3871's, there will be an 'M' rating on them somewhere.
2. Correct
3. The fuses in the switchfuse will more than likely be BS 88's, the switch itself, BS 5419 depending on age. Ottermill is ancient stuff now so I would have thought 5419.
4. The method of protection when that installation was fisrt installed would be EEBADS.
 
Thanks guys also by the way what is the EEBADS stand for.

Aye its great to tap into the fountain of knowledge
 

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
Help with PIR
Prefix
N/A
Forum
Periodic Inspection Reporting & Certification
Start date
Last reply date
Replies
8

Advert

Thread statistics

Created
oldtimer,
Last reply from
Guest123,
Replies
8
Views
2,418

Advert