Hi
Needing help with a PIR.
1. Old wylex type 2 CBs what BS is this an what Ka rating does it have.
2. MEM Memway 3 phase DB with rewireable fuses i take it they are a BS3036
3.The Memway is fed via an 60A TPN switch fuse Oterail make would this have a BS No
4. Method of protection on PIR is this Automatic Disconnection of Supply.
Anyway thanks in advance for any help
Hi
1. Bs3871 normally 6Ka
2. Yes 3036
3. Could be bs60947-3
4. On a PIR pre 17th its EEBADS
1. More than likely BS 3871's, there will be an 'M' rating on them somewhere.
2. Correct
3. The fuses in the switchfuse will more than likely be BS 88's, the switch itself, BS 5419 depending on age. Ottermill is ancient stuff now so I would have thought 5419.
4. The method of protection when that installation was fisrt installed would be EEBADS.
Earthed Equipotential Bonding and Automatic Disconnection of Supply
Took me 3 attempts to spell disconnection.