All done & passed ;)
He went over everything and including the twin and earth sub, but told me that due to all flats being bonded to a gas main riser ( no longer in use but extraneous ) and main water and with all the flats being run in 16mm sq that the 6mm would be fine as there are effectively a large system of parallel paths down to earth and that there are no thermal effect issues of the existing cpc.
 
Got my inspection on Monday Just a pain as so busy and a new inspector so will be having to show I can test etc been down this route 5 times now different assessors.

Should be in your notes guy can test so no probs

Rant over
 