1.
Doing Ze today and getting weird results: 0.97, 1.10, 1.21. (Using Megger 1552).

As I was doing the test, there was a definite arcing type of clicky sound each time down in the region of the the mains head. I couldn't see down there as I was testing as my arms weren't long enough.

However, Zs values on the socket ring were fine, in the region of 0.32 to 0.64 ohm.

How can this be???

I thought it was TN-S, but I'm beginning wonder if there's any earthing facility at all ..... (but there must be).

The main earth conductor (16mm) came from a clamp around the steel conduit within which the L and N from the mains head went to the CU. There was also a strand of steel wire maybe 4mm in diameter from the mains incomer sheath to this clamp. As well as this, the reason I assumed it was TN-S was the absence of an earthing block in the neutral, and the fact that the main earth conductor didn't go looking for a rod, but went to that clamp. Is it TN-S?

2.
And here's another question! There was no water or gas bonding in the house when I got there. The water comes in at the back of the house below the kitchen sink in a tiled (floor) kitchen. To get a 10mm earth from there to the front where the CU is would be cause carnage.

This house is next door to mine in a row of terraced houses. As the two houses share an incoming water feed which comes into mine, splits, then goes through the wall into next door (the house I'm working in), I have taken the liberty of running the 10mm water bonding through the wall to mine and placing the bonding clamp on the incomer in my side. I think there might be a Reg that says this isn't allowed, but is it ok if the water feed is shared between the two houses?

Sorry for the long post, but this has gone from three extra sockets to this! And I was hoping to use it for my NIC annual inspection next week.

If you've got this far .....Thanks for reading it.
 
It is TN-S, to get a Ze reading you need to disconnect the wire from the sheath from the clamp and test.

I had it recently where the Ze in a TN-S was over 8 ohms and told customer to ring supplier, and they came out immediately and sorted it
 
Thanks Johno.

I'm right up against it here. My own fault, I know. This was meant to be a straightforward job - add three sockets, put in 30mA RCD, inspect-test-certify, get NIC Inspector in Wednesday and hey presto.

Now though it's the classic can of worms! No bonding at all and dodgy main earth connection. The reason I didn't do a reccy was a)because it's next door and b)because it has an extension put on a few years ago and I assumed the electrics would have been inspected then. Lesson learnt.

I'm going through the BigRedBook with a fine toothcomb now for info about location of main bonding connection. There's nothing in 411.3.1.2, nor is there anythng in Chapter 54.

Any clues chaps?
 
Hi,

Services bonding should preferebly be within 600mm from where it enters the property, or where practical before any branches. As Johno has said, you will need to do this in the property.

Steve
 

Reply to High Ze with Low Zs, and Location of Water Bonding. in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

Hi All New to this forum, have read the posts on here from google but only recently signed up. I'm having some issues and some input would be...
Replies
13
Views
2K
Hi, while carrying out an EICR at a farm cottage on Friday i came up against a problem early on. Whilst measuring the Ze the reading i obtained...
Replies
22
Views
2K
TNC-S main supply with 16mm swa supplying garage consumer unit from main consumer unit in house, then 4mm swa supplying pond equipment through...
Replies
36
Views
3K
I have been asked to provide a quote for a supply to an toilet block on a campsite. The three phase supply to the campsite is approx. 150m from...
Replies
8
Views
486
Did a eicr on a upstairs flat, there is 1 main bonding cable from the consumer unit, the gas pipe comes from the gas meter outside and up the wall...
Replies
21
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock