Hi, I live in a house that has been converted into three flats. Each flat has a circuit breaker box, but there doesn't appear to be one for the communal lights. We have an issue with the communal lights being permanently on (because of a faulty timer switch). Is it normal for there to be no circuit breaker for it? Any idea how we're supposed to repair the lights? (There also doesn't appear to be an overall electricity switch for the property, just the circuit breakers for each flat).
 
It is not normal and extremely dangerous for a lighting circuit to be installed without any fuse or circuit breaker protection.
It is also incredibly unusual, almost unbelievable that anyone would have installed it in such a way.

It is far more likely that there is a circuit breaker but you just haven't found where it is yet.

Have you contacted the landlord, owner of the building, management company or whoever has responsibility for the communal areas?
 
You say each flat has a circuit breaker box where are the meters? In a communal area cupboard perhaps, I think it likely there is another circuit breaker box in there.
 
You say each flat has a circuit breaker box where are the meters? In a communal area cupboard perhaps, I think it likely there is another circuit breaker box in there.
There is a cupboard with the three circuit breaker boxes (one for each flat) and four meters (one for each flat and the communal areas) ... that's the problem, there's just no sign of anything resembling a circuit breaker or switch for the communal area.
[automerge]1592665035[/automerge]
It is not normal and extremely dangerous for a lighting circuit to be installed without any fuse or circuit breaker protection.
It is also incredibly unusual, almost unbelievable that anyone would have installed it in such a way.

It is far more likely that there is a circuit breaker but you just haven't found where it is yet.

Have you contacted the landlord, owner of the building, management company or whoever has responsibility for the communal areas?
I'm one of the owners, alongside those in the other two flats. There's no sign of a circuit breaker for the communal area, just one each for the three flats (alongside four meters - one for each flat, and one for the communal areas).
 
Can you show a picture of the set-up.
 
  • Like
Reactions: DPG
Can you show a picture of the set-up.
The first picture is the overall setup. The second is a close up of the communal meter (on the left in the picture). Thanks.
Meters 2.jpg
 

Attachments

  • Meters 1.jpg
    Meters 1.jpg
    89.8 KB · Views: 87
Last edited by a moderator:
Have you shone a torch in the cavity to the left and above the communal meter.
 
Follow the outgoing tails from the left hand meter.
 
4 meters 3 flats. The meter on the left must feed something.
 
Thanks. They just lead to the grey box in the top left of the attached image.
There's your answer....looks like a Wylex 2 way Consumer unit.
Unscrew that small cover for the fuse(s).
BUT SWITCH IT OFF FIRST.
 
Last edited:
Thanks. They just lead to the grey box in the top left of the attached image.

Good chance the lights will be fed from a fuse or breaker under that cover on the grey box. From what I can see it looks similar to this.
old fusebox.jpg
 
  • Like
Reactions: Tim345
The little grey box to the left of the flat A consumer unit.
Im sure it has FUSES written on it.
And the white box above flat A? could be a timeclock or something?

It looks to me like the cabinet was built to allow access to the flat CU's but no thought to the DNO fuses or the communal fuseboard.

Who pays the communal charges?
 
  • Like
Reactions: DPG
There's your answer....looks like a Wylex 2 way Consumer unit.
Unscrew that small cover for the fuse(s).
BUT SWITCH IT OFF FIRST.
Perfect - thanks for your help!
[automerge]1592670839[/automerge]
The little grey box to the left of the flat A consumer unit.
Im sure it has FUSES written on it.
And the white box above flat A? could be a timeclock or something?

It looks to me like the cabinet was built to allow access to the flat CU's but no thought to the DNO fuses or the communal fuseboard.

Who pays the communal charges?
Thanks - think I've got this sorted now.
 
Last edited by a moderator:
Why is the LL not sorting it. Are you sure you should be poking about on communal lighting?
 
  • Agree
Reactions: Baddegg
  • Like
Reactions: DPG
The first picture is the overall setup. The second is a close up of the communal meter (on the left in the picture). Thanks.View attachment 58941

The small consumer unit to the left of consumer unit A will be feeding the communal circuits.

When was the last time that mess was inspected and tested by an electrician?
 
See #4, there is no LL
That does not show there is not a LL. It shows that some people have a leasehold on a flat and the lease is to the superior LL. True they may have exercised their right to enfranchise and purchase the freehold however they would have had to form in effect a management company with LL as a legal fiction even if it is themselves. Unless of course they have a not very often used flying freehold.
 
  • Like
Reactions: Baddegg

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Email
Joined
Time zone
Last seen

Thread Information

Title
How to repair switch with no circuit breaker?
Prefix
UK 
Forum
UK Electrical Forum
Start date
Last reply date
Replies
21

Advert

Thread statistics

Created
Tim345,
Last reply from
Vortigern,
Replies
21
Views
2,105

Advert