Is electrical design and testing mandatory?

Let me qualify this with "I know it is" The problem is I have a client who refuses to accept that any and all electrical systems need to be designed properly, installed, tested and commissioned according to the EAWR and BS 7671 and temporary structures (conference/expo sets, marquees, temporary buildings) actually come with more regs (BS 7909) not less and they cannot be put into service without being tested by a qualified electrician.

I invite you all to comment in the hope that advice many electricians is convincing when the advice of three have been ignored.

Thanks B
 
BS7671 and BS7909 compliment each other to ensure all installations are safe and fit for use.

But the overarching legal bit is EAWR, ask your client to explain how these installation fall outside the scope of the EAWR.
 
Is electrical design and testing mandatory?

Let me qualify this with "I know it is" The problem is I have a client who refuses to accept that any and all electrical systems need to be designed properly, installed, tested and commissioned according to the EAWR and BS 7671 and temporary structures (conference/expo sets, marquees, temporary buildings) actually come with more regs (BS 7909) not less and they cannot be put into service without being tested by a qualified electrician.

I invite you all to comment in the hope that advice many electricians is convincing when the advice of three have been ignored.

Thanks B
What do you mean Mandatory BS7671 IS NOT MANDATORY!!
 
Do not allow yourself to be drawn into doing work that you personally feel is unsafe.

EWAR is the one that will get YOU if there is a serious issue.

It may also get your customer but that would be of little consequence if you are locked up and they are fined.

after all the court will possibly believe there story about the contractor said it would be ok cause it was only there for a week.
they will not believe, that a qualified spark did not understand the risks involved and will grill you on why the installation was energised and not up to standards.

it can be a tough one, especially when dealing with an existing customer who pays well.
Bottom line, DO NOT let someone erode your professional integrity.
 
Yeah but testing is... according to EAWR

And yes... probably not a client we will actually work for... I don't want to go to prison.
Although BS 7671 is not Mandatory, to comply with EAWR which is, a legal document, all you need to do is to comply with BS 7671 which isn't, a legal document, to ensure compliance with EAWR. Need I go on and on?
 
Last edited:
@BrianM

Erm, wow.
thanks for the positive feedback but "funny"???? really?

IT WAS NOT meant to be amusing.

if I said what I was thinking, I could get myself banned.

please tell me that you clicked the wrong button, I cant see anything about being jailed as amusing.
 
@BrianM

Erm, wow.
thanks for the positive feedback but "funny"???? really?

IT WAS NOT meant to be amusing.

if I said what I was thinking, I could get myself banned.

please tell me that you clicked the wrong button, I cant see anything about being jailed as amusing.
Pardon, wasn't me that posted a funny
 

Reply to Is electrical design and testing mandatory for temporary structures? in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

I've seen a lot of people on here addressing the online qualifications for access training but not talking about the Apprenticeship aspect. I've...
Replies
1
Views
934
Hi there, Just about to move into a house with 2 small kids and the wiring/electrics haven't been updated in years (hard to know as it's probate)...
Replies
10
Views
2K
We have started a business building garden rooms/caravans/mobile homes under the caravan act. We have only done one so far and I got an...
Replies
3
Views
1K
Hello all, First of all I apologise if this is in the wrong forum, I figured the general forum may be the best bet :) Thank you for taking...
Replies
3
Views
508
We have had a rear extension built on our home, and our builder arranged the electrician for the electric work required. I have established that...
Replies
8
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock