Discuss Is this an acceptable means of earthing ? in the UK Electrical Forum area at ElectriciansForums.net

Also shouldn't the earth wire on the first clamp be looped through under the screw. Not cut ends?
Not acceptable to loop (on my elec course) bonding with a cut cable
.[/B]
But if the 1st pipe is actually the earth then its one cable to feed earth to the house and the second is the only bonding?
Does that make the pipe a MET :)

No its not a reg just considered best practise.
 
We have lots of supplies like that around here. Main tn-s supply into one property, then looped with vir tails in conduit to the next property. Main earth is taken from the first property via the conduit, to the second property. In fact I've been at two jobs in the past week both with exactly this arrangement.
 
Why isn'ta 16mm earth run in the conduit as well? Copper would ge better than steel with 2 clamps involved.
 
Because it was done in the era when nobody ran a copper earth or CPC if there was a steel containment available to do the job, just standard practice. Perhaps it's time to rephrase the question: "If the DNO supply arrives through a steel conduit that gives a satisfactory Ze when tested, is it adequate to terminate the EC to it with a BS951 clamp and consider the installation properly earthed?"

BTW surely that G/Y cable goes behind the wood to the CU and not into the sealing chamber / cutout?
 
What is the earthing system? Is it possible that the DNO have converted it to TNCS and that the earth connections we can see apparently coming from inside the cutout are actually just earthing the conduit?
 

Reply to Is this an acceptable means of earthing ? in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

I'm getting an old fuse board upgraded in an office block. The electrician has just told me that most of the circuits don't have earth cables...
Replies
44
Views
3K
Hello All I was pondering an idea recently regarding the ground connection to my property. At present it has a combined Neutral to earth at the...
Replies
8
Views
1K
Hi, I'm a little confused confused is someone can shine some light on the amendment 2 way of doing IR. I know you have to do one 1st fix at 500V...
Replies
6
Views
2K
I am installing a Victron Quattro in an island mode configuration (in the UK, the DNO is the NG). I will be adding a stand-by generator. My...
Replies
3
Views
1K
Hi all, After months of waiting, the fused neutral cut-out at my parents house has been replaced but I am concerned about the main earth. I...
Replies
6
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock