V

vernam616

Looking to install quite a lot of floodlights for a customer (direct replacement of SONPAKS), been looking at the LED floods which give a good output along with energy saving for the customer

However i have been told by the manufacturer that you cannot use a photocell/retro fit photocell to control the LED flood

Does anyone know a reason as to why? maybe im looking at this in a basic way but surely the photocell is just allowing 240v to pass to the fitting when dusk approaches

thanks
 
Might not be relay output, then the load might be too low for a triac ( i think i remeber something about a holding current with triac ) however I would assume most photo switches have relay outputs so it should work.
 
just about to say that.... ^^^^^

or get a decent set of floods from a supplier that can use a photo cell
 
I have already considered a contactor it just wasnt practical for the application ( like for like replacement, keeping costs down on job etc.. )
 

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
LED Lighting control
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
4

Advert

Thread statistics

Created
vernam616,
Last reply from
vernam616,
Replies
4
Views
1,926

Advert