Hi Emillo83,
Emergency lighting is a safety critical element principle of construction, and is required by law. As the others have mentioned, there is nothing stopping you from installing this, however if anything does go wrong (if there is a fire and this doesn't function properly and injury or death results) then you need to ensure you are capable of defending your position installing it yourself, rather than having a competent professional do the work.
For example, have you done lux level calculations with the proposed lighting, to ensure the light levels conform to the minimum requirements of BS EN 1838, and the wiring system conforms to BS En 50172-4? Do you know that the centre line of the escape route will have a guaranteed minimum light level of 1Lx at every point, and 0.5Lx off the centre line? Have you got direct light on every tread of the staircase? These are just a couple of requirements.
I don't mean to sound critical, its just such an important factor in building safety and often done very wrong. Even if nothing goes wrong, it can still be inspected by the fire authority and you can be prosecuted if the emergency lighting isn't suitable.