In a little pickle any help would be great

i have 3 185 watt panels in a string, for mcs inspection next week just filling out test report ( i know small system but no cash left after all the ££££ gone to get this far )

array parmeters voc 133.8
isc 5.8

string test voc 129
isc 1.6

sun 700r (i think i am reading the meter correctly)
temp was 15c

got this far but its the calc to check if all is ok im a bit lost really

any help would be good

thanks keith
 
Your stated Isc of 5.8A I assume is the STC conditions. So @ 1000W/m2 you should get 5.8A from your string.
When you did your test you measured 1.6A but I'm not sure what the '700r' is supposed to represent.
If 5.8A is @ 1000W/m2 then when you read 1.6A I would have expected an irradiance measurement in the region of 275W/m2 (using the following calculations - 1000 x 1.6/5.8)

The ambient temperature of 15C is not the temperature required to confirm Voc is correct - you need the temperature of the panel itself - although measured voltage of 129V against expected 133.8V looks good enough (<5% error).
 
could not workout what was going wrong . thank you for that it must have been the sun reading i had wrong

many thanks
 

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

YOUR Unread Posts

Daily, weekly or monthly email

Thread Information

Title
little help please with test report p.v
Prefix
N/A
Forum
Solar PV Forum | Solar Panels Forum
Start date
Last reply date
Replies
2

Thread Tags

Advert

Thread statistics

Created
new sparks,
Last reply from
new sparks,
Replies
2
Views
2,769

Advert