Trying to get my head around pv system commissioning sheets ready for future mcs assessment. How do i work out my array parameters Voc (stc) and Isc (stc). How do i find out the dc rating (V) of the protective device and also can anyone explain how string test method annex -2 Voc, Isc,Sun is carryed out and how do i decide the I R test voltage. I would be really grateful if anyone could help
 
parameters ~ Voc (open circuit) volts and Isc (short circuit) amps from module data sheet multiplied for series/parallel connection.
Tests results on the the day ~ Voc and Isc will depend on the "sun" power, so take irradiation measurement~ the norm is to measurse in Watts per meter sq. then compare this with module output data sheet to see if your in the ballpark.
Protective devices have will have a Voltage rating, so if fitted will have to be Voc x 1.25 min.
I R test voltage:
if Voc x 1.25 < 120 then at 250
Voc > 120 < 500 then 500
Voc > 500 then 1000 but can reduce if module has a max allowable voltage less than advised test voltage
 
gsd77 im just filling in first pv array form and havnt a clue? did u find out please??
 
well lets hope so!! general question though! do i need sotware like pv sol? or is sunny design 2 (sma) exceptable to mcs?
 
ok! i thought i had to have all details of first install ie schematic? performance? stuff like that in handover pack?
 
Sure you do - look in the DTI guide its all there for you in black and white, just do what is says in the book and bobs your uncle, once you have MCS then you can concentrate on adding value to the Hand over pack.

Schematics you can get of this forum somewere, do a performance cert on something like word, again the DTI/MIS document tells you what to put - its only the SAP calc.
 
ok thanks for that!! its all getting a bit exspensive!! so if i dont need it at mo then i wont!
 
Not right now IMHO, the DTI has it all in there, if you follow that and the MIS doc then i dont think you can go far wrong. But if you need any guidence just as or PM me i will always help were i can.
 

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
Confused about pv systems commissioning test sheets.
Prefix
N/A
Forum
Solar PV Forum | Solar Panels Forum
Start date
Last reply date
Replies
13

Advert

Thread statistics

Created
GSD77,
Last reply from
powervan,
Replies
13
Views
10,540

Advert