Newbie here, my company has recently taken over a solar site and I have been tasked with fixing the inverter which is a Schneider Zantrex GT500. Support from Schneider has been poor. Anyway, after troubleshooting the AC breaker failure, determined that the under voltage coil was bad so I sent it out to be repaired and tested. The inverter would try to close in the AC side and would fail. I just recently got it back and installed it however while waiting for start up DC voltage(which is 440VDC), I noticed that as irradiance increased my total DC voltage on the controller was dropping. I started around 432VDC at about 670 wm2 and as it got sunnier my voltage lowered to about 414VDC around 1032 wm2. There are 8 combiner boxes with 24 strings each with 12 panels per string. I tested VOC on each string on a few boxes to determine if i had a bad panel somewhere and I did see lower voltages on some strings but I couldn't find any bad panels. I do know that I have to do much more testing but I was curious if anyone has found a problem similar to this where when it gets sunnier and voltage decreases? Just looking for some suggestions as I am new to Solar and very new to DC to AC inverters. I though maybe the MPPT might be malfunctioning but I don't know how to test this. Any help would be greatly appreciated.