Been asked to advise on a rewire. I think on age alone it's advisable but the following points add to the argument.
Installation age approx 60 years.
This is a "forever Home" so although it may test ok how long will it stay so?
Black T&E throughout. Not a reason to condemn alone but adds to the case.
No lighting CPCs
The house is being knocked about and stripped for redecoration.
It's what looks like a looped supply as there are two TN-S incomers and only one fuse, sheaths linked via MET ??2.5mm ish main earth cable. Ideally I'd like a new supply as looking to move the CU, new meter, mains isolator. It's a simple under floor job to run so why not get the mains cable run direct to new CU location?
What disasters do the hive mind anticipate.
Installation age approx 60 years.
This is a "forever Home" so although it may test ok how long will it stay so?
Black T&E throughout. Not a reason to condemn alone but adds to the case.
No lighting CPCs
The house is being knocked about and stripped for redecoration.
It's what looks like a looped supply as there are two TN-S incomers and only one fuse, sheaths linked via MET ??2.5mm ish main earth cable. Ideally I'd like a new supply as looking to move the CU, new meter, mains isolator. It's a simple under floor job to run so why not get the mains cable run direct to new CU location?