Doing a pir in a factory today and was testing a machine and found that there was no earth on it, swa was not glanded in correctly at the machine end, only shoved through a hole and taped up the circuit had a seperate 16.0mm g/y but no earth contonuity?
After finding a 100A isolator hidden behind some racking i found this in the bottom. IMG00181-20101118-1051.jpg L/H connector is on 6mm earth screw on bottom of isolator, middle cable is incoming cpc, L/H cable is outgoing cpc, whoever installed it must have thought that the connectors were made of some sort of magic plastic that would give the earth continuity?
this factory was last inspected 4 yrs ago and wasn't found then, machine has been in 10 years. The machine was earthed through parrallel paths as it had another 63A TP supply on it, would suspect only earth loop carried out in past and rest of reading guessed!!
 
Last edited by a moderator:

Similar threads

S
  • Question Question
Replies
6
Views
2K
Australia
Engineer54
E
V
  • Question Question
Replies
14
Views
2K
Australia
GLENNSPARK
G

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
Magic connectors
Prefix
N/A
Forum
Australia
Start date
Last reply date
Replies
4
Unsolved
--

Advert

Thread statistics

Created
glynnis,
Last reply from
brucelee,
Replies
4
Views
1,516

Advert