Richard
Hi,
Changing an old Three phase board in a school today which feed off-peak storage heating and underfloor heating. The supply Is TN-S.
The board were fitting in a Crabtree Loadstar, and comes supplied with a three pole isolator.
As this is effectivly the main board for the effected circuits, should the main switch also switch the neutral? Looking at BS7671
537.1.4 - A main switch intended for operation by ordinary persons, e.g of a householder or similar, shall interupt both live conductors of a single phase supply
537.2.1.1 - Every circuit shall be capable of being isolated from each of the live supply conductors. In TN-S or TN-C-S, it is not neccesery to isolate or switch the neutral conductor where it is regarded as being reliably connected to earth by a suitably low impeadance.
Just what to check i'm correct in thinking a three pole isolator will be ok.
Thanks
Changing an old Three phase board in a school today which feed off-peak storage heating and underfloor heating. The supply Is TN-S.
The board were fitting in a Crabtree Loadstar, and comes supplied with a three pole isolator.
As this is effectivly the main board for the effected circuits, should the main switch also switch the neutral? Looking at BS7671
537.1.4 - A main switch intended for operation by ordinary persons, e.g of a householder or similar, shall interupt both live conductors of a single phase supply
537.2.1.1 - Every circuit shall be capable of being isolated from each of the live supply conductors. In TN-S or TN-C-S, it is not neccesery to isolate or switch the neutral conductor where it is regarded as being reliably connected to earth by a suitably low impeadance.
Just what to check i'm correct in thinking a three pole isolator will be ok.
Thanks