an mccb main switch then mcb's or mccb's feeding sub boards.

when the shower/sockets/lights trip it doesnt trip every other mcb does it, same thing

No it's not the same thing, you suggested installing a DB and feeding sub mains from MCBs in that DB.
That puts the final circuit MCBs on series with the distribution circuit MCB, this will may not discriminate in the event of a fault on the final circuit.
 
No it's not the same thing, you suggested installing a DB and feeding sub mains from MCBs in that DB.
That puts the final circuit MCBs on series with the distribution circuit MCB, this will may not discriminate in the event of a fault on the final circuit.

That is what I thought I was replying to earlier, tis Friday night though ;)
 
the installation is a 3 phase incoming, however only one the phases used which goes into a henly block then splits into 3.

so best practise would be to place the isolator before the henly block so the main switch covers the whole installtion.

oh and they reasons why the main switch cant be a RCD switch.
 
the installation is a 3 phase incoming, however only one the phases used which goes into a henly block then splits into 3.

so best practise would be to place the isolator before the henly block so the main switch covers the whole installtion.

oh and they reasons why the main switch cant be a RCD switch.

Do you really need to ask this??
 
Read 314.1 in the BGB then have a think why you shouldn't fit a RCD main switch on a TN system.

potentially if we had nuisance triping it could be a killer for this type of business. so rcd protection as a main switch is a no no. RCBO protection for socket circuits is needed so only that circuit in question would disconnect instead of whole supply
 

Reply to main switch question in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

Can a domestic consumer unit feed another consumer unit, via the Main Switch. Details are: domestic property with 100A single phase supply...
Replies
9
Views
484
Hi all. I have been asked to take over a job an electrician has started, and has moved abroad. The house is a big mansion, with a 3PH supply...
Replies
49
Views
4K
Hi there, Any advice on this would be greatly appreciated! (Note, this is not a DIY, I'm using a fully qualified electrician, just posting here...
Replies
8
Views
743
D
Hi, I have received conflicting advice about Main Isolator Switches and would appreciate forum member's help to plan a way ahead. Looking to the...
Replies
5
Views
2K
Deleted member 155212
D
Hi I have a job where customer has two families one families lives upstairs and one family will live downstairs. As the property is going through...
Replies
12
Views
767

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock