hawkal

The main tails are sized based on the rating of the main fuse so that regardless of the usage you must use what is standard? I just ask for some different opinions because my boss will probably try to bs his way out of buying some main tails and I need some more ammunition.
 
Last edited by a moderator:
Taken from the OSG.... Page 17

2.2.3 Meter Tails
These are part of the consumers installation. They should be insulated and sheathed or insulated and enclosed in conduit or trunking. They are provided by the installer.

Polarity should be indicated by the colour of the insulation and the maximum cable size should be 25mm. The distributer may specify the maximum length and the minimum cross sectional area.

Where the meter tails are protected against fault current by the distributers cut out the method of installation, maximum length and minimum cross sectional area must comply with the requirments of the distributer.

Hope thats helps,

:D
 

Similar threads

D
Replies
5
Views
4K
UK Electrical Forum
Deleted member 155212
D

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
main tails 25mm regardless (100A mf)?
Prefix
N/A
Forum
Electrical Wiring, Theories and Regulations
Start date
Last reply date
Replies
1

Thread Tags

Advert

Thread statistics

Created
hawkal,
Last reply from
Sparky83,
Replies
1
Views
1,624

Advert