Hi all,

Ive just installed a new split load CU, lots of old circuits in the house, every circuit works ok except one (a kitchen ring, recently installed but not by me).

The problem is this:
I conect the lives of the kitchen ring to the mcb and the earths to the earth bar, but when i touch the neutrals to the neutral bar the RCD trips.

I swapped this circuit over to the other RCD side and it happens again.

If I remove the earths of this circuit I can happily connect the neutrals with no tripping, but soon as i touch the earths to the earth bar it trips the rcd again.

Insulation resistance is good.
But there is continuity between earth and neutral on this ring.

Ive had every socket off the wall and they have been wired correctly.

What am i missing, i will be going back in the morning so any tips pointers wil be very much appreciated as Im tearing my hair out!

Thanks,

Simon.
 
had similar.was outside socket spurred off kitchen ring. So called IP65 box cotaining extn. lead feeding garden lights and pond pump. opened box. hair dryer and resealed. end of N-E fault
 
It will more than likely be a neutral touching the KO box, I would just unscrew all easy to access sockets first and keep my fingers crossed.
 
and look for nails in walls hanging pics etc.!!
 
Ok sorted it today.
i split the ring down to the last couple of single skts, disconected them tested and the problem went away, re conect the skts and everything is ok, could not see any niks in the insulation, scratched my head, wired up the CU and no problem. All good! moisture perhaps? an invisible gremlim?? god knows but now its fine??
Thanks for your replys!

Simon.
 
Box screw shorting on the neutral possibly

Sounds favourite, had two of these last week on the same cct. Funny thing was she'd just got new wireless phones and they hadn't been working right, once I cleared the faults they worked fine, whats that all about ?
 

Reply to Major problem - am I missing something?? in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

Please advise what I should test / check next. My usual qualified electrician who did all of the work here is in Ireland for 4 weeks and not...
Replies
45
Views
3K
Hi All Happy new year to all! First post but long timer lurker, so thanks for all the previous help! Just wanted to clarify something I have...
Replies
7
Views
842
During some testing I found a N-E IR fault on the kitchen lights of 0.1Mohms. I also found a N-E IR fault on the ring sockets, again 0.1Mohms...
Replies
58
Views
8K
I'm not sure what's going on with my kitchen light. I've replaced an old 28W CFL fitting with a new 4 x LED GU10 fitting (a cheap one from...
Replies
11
Views
1K
My circuit panel has two banks of breakers, each bank protected by an RCD. One of these RCDs has been problematic in that it trips intermitantly...
Replies
12
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock