I have a building with row after row of light fittings where the containment between in 8-10 inches long metal conduit (20mm).
This metal conduit is between and incontact with the plastic body of the light fitting and protects the single core cables.

I have said the conduit does not require to be bonded.
Half the people who have become involved with this side with me half against.

I have proved the conduit is not connected or incontact to earth with an insulation test (result above 500meg) and so I say it does not require bonding.

Where is it in black and white where it says it does require it? Or better still where it doesn't need it !

With thanks
 
It's not an extraneous conductive part therefore it does not require bonding.
It is an exposed conductive part and therefore it requires earthing....411.3.1.1
See definitions of the above in part 2 of 7671.
 
Snag 24 of snags and solutions 4th edition says where unsheathed cables the conduit needs to be effctively earthed. However if sheathed cables are used it may not be necessary to earth the conduit.
 
As others have stated these short conduit lengths don't need bonding, they need ''earthing!! I take it that these short conduit lengths, (and they do seem very short) are individual conduits connecting the plastic light fittings via couplings and male bushes, and it seems you have scores of them...lol!! Well, it will at least keep you busy either fitting earthing nuts or banjo arrangements and linking them all out with a CPC!! ...lol!!!

Who was the idiot that purchased Plastic body lighting fittings with a metal conduit containment system in place.
 
personally i think swopping out such short legnths of conduit with plastic will be quicker and neater than faffing about with banjos and wire links.
 
Apologies for not posting earlier but some reason thesite keeps throwing me out !!!!
Help for Heroes is now 20pound better off.
Best to be sure than to blindly plough on being wrong!! And I was wrong.

Who decided plastic and metal…. no idea! Properly down towhat was left in the bin after another job/jobs. CE fitting with UL metal pipebetween them.

UL fitting (inch) forced in to CE kit, 120v 60hz socketsrunning 230v 50hz, 120v breakers on 230v. Single phase UL boards 120v on 400v.It’s a never ending job but the pay is good.
 
Ahhh, your in Afghanistan then ...lol!!

I was on a project once, trying to utilise Yank conduit into UK back boxes it doesn't work does it!! lol!! , The Yank conduit soon got thrown out and metric bought in!!!

I take it, ...it is the crappy light gauge conduit that's been used, the one where connections between couplings and end fittings are by means of set screw, similar to our old slip 1/2'' conduit. Well if your now going to earth all these short bits of pipe, at least the Yanks have earthing nuts to fit those end fittings...lol!!!
 
Split wedges I think they're called ! Undo the locking nut and slide this spade behind the locking nut and tighten, carry onseveral 100 times !!!!!!!

The conduit made from reclaimed Indian take awaycontainers, be nice if we could go 100% CE (UK) but the people who buy the kit get a percentage on every $ they save.

CE is more expensive and ALL the company's try to 'buy USA first' as they get money back from the Government and it shows they are true patriots and so they will get the next billon $ contract!!
 
Last edited:
As a fix for this situation would it be possible to "sheath" the singles with some split 16mm plastic flexible conduit, negating the need to dismantle any of the installation apart from removing the covers and load trays of 1/2 the fittings?
 
> ...protects the...cables. ...the conduit is not connected or incontact to earth with an insulation test (result above 500meg) and so I say it does not require bonding.

The conduit is for protection? Try it. Smash it with a filing cabinet or over-enthusiastic ladder. Now Meg it. If you bash it hard enough, the wire insulation is smooshed, and now live wires touch the conduit.

If conduit is PVC, no shock will result.

If conduit is metal, the exposed metal is now a shock hazard. And very unexpected for the next guy who leans an aluminum ladder up there and steps-off from damp concrete floor.

If conduit is metal AND appropriately bonded back to the designated Earth and service common, the first bash will cause a short which will blow a fuse, making the wires dead/safe and forcing cautious investigation.

In general "ALL" touchable metal around the place "should" bond to electric common.

Even metal siding: there was a case of a nail through aluminum siding into a live wire. Nobody noticed until a painter was zapped off his ladder (actually the owners noticed a tingle but did nothing). If the siding had been bonded, that nail would have darkened some circuit and forced investigation. (If the coincidence were not noted this could be a very tedious job.) I admit I never see a bond on siding. Or metal roofing unless good lightning protection has been done.

That's general principles of decent wiring.

I'm not not an expert in fine points of the rules. Wirepuller posted chapter&verse "exposed conductive part ....411.3.1.1". It's exposed, it conducts, your first thought should be "bond it!"

Local custom and interpretation will vary. If it is a HIGH ceiling and very unlikely to get bashed hard enough to damage insulation through conduit, maybe bonding can be omitted. If the internal cable is rated rugged to withstand great abuse (what Malcolm asked and Pockets Snag-ed), perhaps bonding can be omitted. There's a new residential garage on my street 3 meters high inside, and I know our local inspector will not climb that high to check.

And if you are in Afghanistan then the occupants may face dangers worse than some live pipe on a ceiling. Of course we hope and pray that the odd blown fuse is the worst that ever happens in future.

> "sheath" the singles with some split 16mm plastic flexible conduit

I would say: if the conduit "can" be bashed hard enough to smoosh the cable insulation, the flex-tube does not add enough extra protection to count for much. Obviously a local inspector might deem it good enough in a marginal case.
 

Reply to Metal Conduit (8-10inch) between PVC strip lights...... Another Bonding Question in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

BMS installers have attended. After fitting the panel they also replaced the aged lighting in the boiler room with 6ft LED battens as instructed...
Replies
5
Views
925
A recent discussion on conduit choice wandered over to pros and cons of the 'conlok' style and a link was posted to one of the Efixx videos in...
Replies
29
Views
4K
I am going to need to install a small amount of galvanised steel conduit, leading down to perhaps 4 sockets and a light switch. This is in a...
Replies
38
Views
4K
Hi guys I have some industrial lighting circuits to wire in a workshop and was after some fresh ideas/suggestions as to how i could best do this...
Replies
12
Views
1K
Hi All. What is the best/preferred method when connecting 20mm conduit to a back box of a socket on an outside wall ? I am connecting a BG...
Replies
10
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock