Good evening,
1) Is the motor current on the nameplate always the full load current: the maximum current the motor can draw without there being damage to its winding insulation.
2) Often in motor books, I see the term nominal current? is this the current that the motor draws under normal operating conditions under load?
3) What the the motor rated current? is this the same as the FLC?
Thanks,
Ewan
FLC on the plate is the current the motor will draw at rated voltage and frequency, delivering rated output power. Most motor standards require the motor to withstand small intermittent mechanical overloads, and allow for a tolerance on the supply voltage. So under some conditions, the FLC might be exceeded without damage to the motor.
I would read all these terms with similar meaning, although I suppose there might be subtle differences in the definitions according to context and whether any particular standard is being referenced.
Feeling better Lucien?
Not a great day actually Pete but I'll say more about that in the Arms thread!
Reply to Motor FLC, Rated current, running current and nominal current. in the UK Electrical Forum area at ElectriciansForums.net
Hi Guys, Is my understanding of why it is bad for a star/delta motor to be stuck in star correct? 1) Star delta starting is used as a method of...
5K
I have a pressure washer that I got as part of "a good deal", actually an exceedingly good deal as I later found out. I've had it a while, I guess...
I want to operate 3 lighting set up using metal halide lamps for studio works or cinematic projects in the future. as of now i have got two...