OK answering a few of these...
The supply to the power supply was changed i was waiting for the brown to come in to stock it was due in the next morning i just put it in to test the panel out.
The Black 400ac supply to the contactor etc I labelled cruidly using a dymo labeller with L1, L2 and L3 around them. I wasnt allowed brown and grey.
As for the 24v wiring i am not familair with the suitable colours for 24v dc I will read up on this i promise but yes in hign site it could be much better i will take this into account if i ever make a panel again.
The PSU is 10A.
I suggested a small PLC but it was rejected by the powers that be.
I have spot on schematics. I have checked them three times but they are in the machine now not with me.
As for risk assesment in all honesty i dont know the extent the checks etc.
Today i had to make some modifications to an exsisting panel by removing the DOL forward and reverse starter and replacing it with a VSD i caused a bit of a fuss when i went and bought a numbering kit on account from the wholesalers. But i refused to do it any other way. I kept the same colour wiring as the exsisting panel. I kept the 400ac supply and the supply to the motor the same numbers and suitably numbered the control wires. The machine is not back in service yet. the only problem i have is no professional way of updating the wiring diagram. But to the show part of the struggle i am up against my boss came along and said oh ive soldered some wires on the potentiometer for you he mounted it in the front half of the panel while im working in the rear he then goes can you see the wires poking through to find he was soldered a bit of old three core 1mm flex on to it that he had cut off an old work lamp. I honestly couldnt believe it. I waited for him to go and i removed it resolding on some 0.5mm tri rated insulating the terminals with heat shrink.
If i cause to much of a fuss about things i get taken off jobs and put on greasing duty's etc which means i learn nothing...
I am glad of my job and i do like many aspects of it im in a situation where i completed C+G 2330 full time course at college and only 3 out of 23 got jobs. and one of them is working for a compressor repair company doing more pipe work than anything. So i see myself as fortunate as ive got a little experiance under my belt. I am always open to advice an will always question something if i dont think its right.
Thank you everyone for your advice and the people who has posted pictures up of there panels i like them i hope one day i will have the knowledge to build a panel to that standard.
Ash
Firstly, thanks for showing your work.
Secondly, holes are rightfully being blown into this example!
You have stated you are not a panel building company... who has verified your circuit design in relation to the Press risk assessment?
Presses... are they covered by special regulations?
Your 400vac (assumed as no signs) feed wiring is in black... your +24vdc is in black... your switched neutral is in blue... your PSU supply (230vac) is in blue... your -24vdc is in blue... You say you want to raise standards... DO IT BY ADHERING TO CURRENT STANDARDS.
Is it an earthed ELV control circuit?
Your lack of wire numbers may be omitted assuming your schematics are spot-on! I take it you have schematics... if so are they computer drafted?
What are you powering with that PSU? It's huge. What is it rated at? 10 or 20A?
These days anything over four relays should be replaced with a programmable logic block or smart relay... thats not to say it must be.
Safety relay? To what safety category have you installed to? Are external monitoring contacts used as part of resetting the light barrier?
What tells you that the motor DOL has tripped? If it alerts the operator then it prevents him fiddling when he can't start the m/c.
Are we to assume all your field wiring leaves from the top of the panel?
I'm not keen on your control wiring passing so close over the supply of the isolator.
Your last sentence... they should not be left wanting!
Please show a photo of your schematics.
regards
s.f