Could some one give me a simple explanation why a trip will not blow on a Pme system and on others and is this dangerous
 
had this yesterday on a TN-S. both RCDs failed to trip on test button and with MFT. found the cable responsible and dissed it, both RCDs now tripping fine. further investigation next week as 1. the cable is short and disappears behind meter board. 2. no idea what the cable feeds as nothing seems to have stopped working.
 
had this yesterday on a TN-S. both RCDs failed to trip on test button and with MFT. found the cable responsible and dissed it, both RCDs now tripping fine. further investigation next week as 1. the cable is short and disappears behind meter board. 2. no idea what the cable feeds as nothing seems to have stopped working.
it`l be for a bypass...
 
it`l be for a bypass...
nope. it goes into the wall and upstairs. it's a 7/029 T/E. possibly for immersion that's been removed. will find out next week.
 
Could some one give me a simple explanation why a trip will not blow on a Pme system and on others and is this dangerous
Sorry lads what I meant to say was way does a RCD not blow when I have a dead short between neutral and earth on a pme system
 
RCD will only trip if there's current flowing down to earth. If there's no load on the RCD it won't trip. Other option is that it's faulty, if you ramp test it you'll know for sure.
 
Are you asking why an RCD won't trip when you have Earth-Neutral link at incomer (as per PME/TNCS)?

If so this is because the RCD only monitors the circuit it is protecting (on the load side of the unit)

There is plenty of literature etc around explaining in detail how RCDs work - if you are in training it's worth a look.

If I misunderstood your question then ignore!
 
  • Like
Reactions: 2 people
It's like why dies it keep tripping when applying a load... But you have got the grey as the earth instead of neutral......, I know
 

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
Neutral / earth fault
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
12

Advert

Thread statistics

Created
vbyrne,
Last reply from
i=p/u,
Replies
12
Views
2,598

Advert