This was in the draft for the 18th:
542.1.201 The main earthing terminal shall be connected with Earth by one of the methods described in Regulations 542.1.2.1 to 3, as appropriate to the type of system of which the installation is to form a part and in compliance with Regulations 542.1.3.1 and 542.1.3.2.
Additionally, there shall be an earth electrode, supplementing any earthing facility provided by the distributor, in accordance with one of the requirements of Regulation 542.2.3, to prevent the appearance of a dangerous touch voltage in the event of the loss of the main connection to Earth.
542.1.201 The main earthing terminal shall be connected with Earth by one of the methods described in Regulations 542.1.2.1 to 3, as appropriate to the type of system of which the installation is to form a part and in compliance with Regulations 542.1.3.1 and 542.1.3.2.
Additionally, there shall be an earth electrode, supplementing any earthing facility provided by the distributor, in accordance with one of the requirements of Regulation 542.2.3, to prevent the appearance of a dangerous touch voltage in the event of the loss of the main connection to Earth.