I have a 20m 16mm t & e cable run up boxing through loft and down boxing in ( ref method c) . The new CU I’m coming from has been put in by a cowboy , rough , no certs etc . There is spare ways but I’d rather come of Henley blocks to isol so I’m just signing off my own work . Question is do I fit a 63a rcd at source and an unprotected CU at other end , or preferably a 60a switched fuse supplying dual red CU ? Just bit worried about feed not being red protected ? Any opinions much appreciated
 
I have a 20m 16mm t & e cable run up boxing through loft and down boxing in ( ref method c) . The new CU I’m coming from has been put in by a cowboy , rough , no certs etc . There is spare ways but I’d rather come of Henley blocks to isol so I’m just signing off my own work . Question is do I fit a 63a rcd at source and an unprotected CU at other end , or preferably a 60a switched fuse supplying dual red CU ? Just bit worried about feed not being red protected ? Any opinions much appreciated
Sorry RCD not red
 
t?e feed would only require RCD protection if:
1, buried in wall < 50mm deep.
2. on a TT earthing system.
 
Will the submain be within 50mm of the surface of the walls? If so you need a RCD

If not you probably don't.

As for coming off the existing CU ........ your EIC covers what you state, so whats the concern?
 
If twin and earth is installed in or through a partion made from metal frame then it requires 30mA RCD protection...like the metal frame they chuck up for stud work walls on newbuilds.
Or as an alternative to rcd protection by a 30mA rcd, you can use earthed containment or a cable with a metallic sheath connected to earth like swa
 

Reply to Opinions please on 20m 16.0mm run in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Long time lurker so this may be my first question. I am a qualified electrical engineer, but in aeronautics not domestic installations, and I may...
Replies
21
Views
9K
I’d like your opinions on a scenario I’ve come across. A certificate was produced which contained errors and while there were still faults on the...
Replies
9
Views
2K
Hi Guys I have been following this forum over a number of years reading endless discussions and picking up things along the way. I am a JIB gold...
Replies
9
Views
3K
Hopefully someone wiser than me can help explain some odd measurements I’ve taken at my own home. This is a long read, I’ve tried to give as much...
Replies
21
Views
4K
Hello i've recently just had a re wire done on a three bed semi house, Ive noticed a few things im not 100 percent on ive spoken to the firm that...
Replies
24
Views
5K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock